A dc-rated shunt trip breaker @ 250A (Blue Planet / OB Radian cabinet
breaker) would do the trick if they exist. The trip device could be mounted
outside.

On Fri, Jan 27, 2023 at 3:55 PM William Miller via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Glenn:
>
>
>
> As I wrote, a DC disconnect is required.  Here is an excerpt from the Q&A
> with the building official:
>
>
>
> 4.   Will you be requiring an external disconnect to disconnect the AC
> output of the inverter system from premise wiring?
>
> Yes, as required per 230.85
>
> 5.   Will you be requiring an external disconnect to disconnect batteries
> from the inverters?
>
> Yes
>
>
>
> If the DC disconnect was not required I would not be wasting everyone’s
> time with my post.  I try to be careful about that, researching on my own
> before posting and trying to make my questions very clear.  I also try not
> to embarrass myself with dumb questions, but that does happen occasionally…
>
>
>
> William
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Glenn Burt via RE-wrenches
> *Sent:* Friday, January 27, 2023 11:46 AM
> *To:* William Miller via RE-wrenches
> *Cc:* Glenn Burt
> *Subject:* Re: [RE-wrenches] Remote battery disconnects
>
>
>
> Does the AHJ really want the batteries disconnected from conductors, or
> does he really just want the inverters to stop operating and producing AC
> within the house?
>
> Obviously there is a big difference here and it may be changing as the
> code evolves.
>
>
>
> -Glenn
>
> Sent from my 'smart'phone, so please excuse typos and spelling errors.
>
>
>
> ------ Original message------
>
> *From: *William Miller via RE-wrenches
>
> *Date: *Fri, Jan 27, 2023 2:26 PM
>
> *To: *RE-wrenches;
>
> *Cc: *William Miller;
>
> *Subject:*[RE-wrenches] Remote battery disconnects
>
>
>
> Friends:
>
>
>
> We have a large-ish residential off-grid system install coming up.  The
> AHJ has said they will require a remote battery disconnect.  I suspect
> there will be fire sprinkler controls and a pressure pump that would become
> inoperable if this system were engaged.  In this case we will apply for a
> waiver.
>
>
>
> The last time this was discussed here as far as I can find was October of
> 2020.  At that time no one suggested any specific battery disconnect
> equipment.
>
>
>
> To further clarify my needs:  There will be 4 or 5 Radian 8048 inverters
> (5 or 6 4/0 battery circuits, ~350A each) and two 175 amp PV recombiner
> outputs.  That is 6 poles of high amperage DC disconnects.
>
>
>
> The battery array will be either a UnigyII VRLA or a lithium of a brand
> yet to be determined.  In the case of lithium we will look for a system
> that can remotely enable a BMS shutdown.  In the case of a VRLA lead-acid,
> we will not have that luxury.
>
>
>
> I have done some considerable research and have not found viable, high
> amperage, remotely activated shutdown equipment.
>
>
>
> I am wondering what hardware others may be using to achieve remote battery
> disconnecting in these types of cases..
>
>
>
> William
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 

*Kirk Herander / **kirkh@vermont.solar <kirkh@vermont.solar>*

*Owner|Principal, VT Solar, LLC*

*Celebrating our 32st Anniversary 1991-2023!!*

dba Vermont Solar Engineering

802.863.1202
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to