Thanks to everyone, the setting I had said AC coupling No. I did not
realize that a firmware upgrade could enable that. I think it is best
to try frequency shift for this particular case. Thanks again to
everyone. Chris
On 11/24/2021 12:38 PM, Tuss, Lones wrote:
Hello Chris
Sorry for the slow response I foolishly took a couple of days of
vacation.
I see this system is on Optics. The GS4048A inverter can do AC
Coupling with frequency shift. It will need to be upgraded from the
current rev of 001.006.063 to 001.007.070 below is a link to that
firmware.
https://outbackpower.com/resources-mobile/technical-support/firmware-updates/item/radian-series-firmware-updates
Once the new firmware is installed will need to change the default
Installer password of 1732 to a different 4 digit number after doing
so In the inverter you can go to the menu and enable AC Coupling.
Below are instructions for changing the default Installer Password.
https://outbackpower.com/downloads/documents/system_management/mate3s/mate3s_programmingguide_web.pdf
please see S-16 in the manual above.
Below is a link to the AC Coupling App Note
https://outbackpower.com/downloads/documents/appnotes/ac_coupling_radian.pdf
I too speak English as my native foreign language below is a link to
Fowlers Modern English Usage
It has helped me to spoke more lucidly and communicate more better.
https://www.amazon.com/s?k=fowlers+modern+english+usage&crid=3AUWAC3TGDBWQ&sprefix=fowlers+%2Caps%2C277&ref=nb_sb_ss_ts-doa-p_2_8
<https://www.amazon.com/s?k=fowlers+modern+english+usage&crid=3AUWAC3TGDBWQ&sprefix=fowlers+%2Caps%2C277&ref=nb_sb_ss_ts-doa-p_2_8>
Thanks for using OutBack
Chris you have my # if you have questions.
Have a good Thanksgiving and Stay Safe.
Take Care All
*From:* RE-wrenches
<re-wrenches-boun...@lists.re-wrenches001.007.070.org> *On Behalf Of
*Christopher Warfel
*Sent:* Tuesday, November 23, 2021 9:40 AM
*To:* August Goers <aug...@luminalt.com>; RE-wrenches
<re-wrenches@lists.re-wrenches.org>
*Subject:* Re: [RE-wrenches] Rapid Shutdown Control for a System for a
Multimode System Adding an Array to a Subpanel in Garage
*CAUTION:*This email originated from outside of the Company. Do not
click links or open attachments unless you recognize the sender and
know the content is safe.
It was tough for me to figure out how to write my email and not make
it confusing.
What I am worried about is the microinverter system operating when the
utility goes down and the microinverters continuing to operate and
charge the batteries as a load. I need to disconnect the
microinverter circuit only when the batteries are fully charged in
grid isolated mode. All the ways I can think of that would normally
work to deenergize the microinverters automatically based upon battery
voltage won't work. I can submit a drawing if that would help. I am
trying not to run another conductor circuit from the house to the
garage. I realize that would solve the problem, but it is an
expensive solution. English is my foreign native language.
On 11/23/2021 10:39 AM, August Goers wrote:
Hi Chris - If I'm following you right, you have a PV system on a
detached garage that ties into a backup subpanel also in the
garage? The code only requires the RSID (rapid shutdown
initiation device) to be on the exterior of the building. Would it
work to put the RSID on the garage exterior? You could route your
PV circuits to a switch or switches on the exterior of the garage
on the way down to the sub it ties into. You could also use a
shunt trip breaker(s) for the PV circuit(s). If for some reason
you need to have the RSID on the main house, it gets trickier.
Might need to trench?
August
Luminalt
On Tue, Nov 23, 2021 at 7:24 AM Christopher Warfel
<cwar...@entech-engineering.com> wrote:
I would appreciate ideas on how to shut down a proposed
microinverter system on a garage that is 100% serviced by an
Outback Radian multimode system in the main building that has
the garage on the back up service panel in the main building.
Garage has a MLO subpanel that is connected to the multimode
back up service panel that is in the main building.
If grid goes down, we need to disconnect the microinverter
array so it does not overcharge the battery system. If we use
the battery voltage relay, we will take out all the garage
circuits, which would disable its heating system, etc. We just
want to disconnect the microinverter circuit in the garage
subpanel.
Does anyone know of a product that could do this. I would
imagine a transmitter, or perhaps something else besides a
microinverter array?
Thanks for any help. Chris
--
Christopher Warfel
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978
<https://protect2.fireeye.com/v1/url?k=b5daa01b-ea4198e0-b5d9a990-861a44d80f79-8d6d4e72be5eadfb&q=1&e=419d5d1e-c0ac-4d3f-ad1a-8cfab76f8c9b&u=http%3A%2F%2Fentech-engineering.com%2F>
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
<https://protect2.fireeye.com/v1/url?k=b8b7ead7-e72cd22c-b8b4e35c-861a44d80f79-a7380300fe73d86f&q=1&e=419d5d1e-c0ac-4d3f-ad1a-8cfab76f8c9b&u=http%3A%2F%2Fre-wrenches.org%2F>
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
<https://protect2.fireeye.com/v1/url?k=c48af253-9b11caa8-c489fbd8-861a44d80f79-4310075dc69a7106&q=1&e=419d5d1e-c0ac-4d3f-ad1a-8cfab76f8c9b&u=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org>
There are two list archives for searching. When one doesn't
work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
<https://protect2.fireeye.com/v1/url?k=7727c68b-28bcfe70-7724cf00-861a44d80f79-cea6b969f07330fd&q=1&e=419d5d1e-c0ac-4d3f-ad1a-8cfab76f8c9b&u=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org>
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
<https://protect2.fireeye.com/v1/url?k=725c0d09-2dc735f2-725f0482-861a44d80f79-954c92e3067c4765&q=1&e=419d5d1e-c0ac-4d3f-ad1a-8cfab76f8c9b&u=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm>
Check out or update participant bios:
http://www.members.re-wrenches.org
<https://protect2.fireeye.com/v1/url?k=94b19eb0-cb2aa64b-94b2973b-861a44d80f79-60c1cb03e533eee0&q=1&e=419d5d1e-c0ac-4d3f-ad1a-8cfab76f8c9b&u=http%3A%2F%2Fwww.members.re-wrenches.org%2F>
--
Christopher Warfel
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978
<https://protect2.fireeye.com/v1/url?k=29e1c951-767af1aa-29e2c0da-861a44d80f79-821d84c651c96860&q=1&e=419d5d1e-c0ac-4d3f-ad1a-8cfab76f8c9b&u=http%3A%2F%2Fentech-engineering.com%2F>
This email and any attachments may contain confidential information
that is intended only for the recipient(s). If you have received this
email in error, please notify the sender and delete it from your
system. Any views or opinions presented in this email are solely those
of the author and do not necessarily represent those of the company or
its affiliates. This email does not constitute an agreement to conduct
transactions by electronic means and does not create any legally
binding contract or enforceable obligation in the absence of a fully
signed written contract. The recipient should check this email and any
attachments for viruses. The company accepts no liability for any loss
or damage caused by software viruses. If you are the intended
recipient and you do not wish to receive similar email(s) from us in
the future then please notify the sender. Please consider the
environment before printing.
--
Christopher Warfel
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978
<http://entech-engineering.com>
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org