William, our city inspectors have moved a bit into this direction for some 
inspections... asking for specific photos fairly similar to the list you were 
given. 
While I feel that the inspection process on typical residential (and commercial 
of all sizes, for that matter) often, but not always, falls terribly short of 
adequate, in my opinion, I agree with you that the system you described 
warrants a closer, in person inspection.  I would think a follow-up phone call 
to ask questions would at least help a bit. Maybe if you have (Code) questions 
about what you did then you should request one?

Cheers,

Benn Kilburn
SkyFire Energy
780-906-7807

> On Mar 31, 2021, at 10:48 AM, William Miller <will...@millersolar.com> wrote:
> 
> Friends:
>  
> We just finished a grid-tied project that included a pretty complicated 
> service upgrade.  The project is in Monterey County, California.  The site is 
> pretty remote on the south end of the Big Sur coastline and Highway 1 is 
> closed (as is not uncommon) to the north with a washout.  This makes it time 
> consuming for an inspector to reach the site, but even without the washout 
> the travel time is measured in hours.
>  
> Days in advance we scheduled the final inspection on the building department 
> web-site as is SOP and were awarded a slot for yesterday.  Yesterday morning 
> an inspector called at 7:30 AM to announce they were too busy to make the 
> appointment.  Instead I was directed to take a series of photographs to 
> verify the validity of our installation work.  Below is the list they 
> provided.  Note how vague the requirements are, particularly the fifth one.  
> I was told that this process will be standard operation procedure for the 
> County of Monterey in the near future for solar installs. 
>  
> This seems wrong to me.  I can’t believe that any collection of photographs 
> can accurately portray if even the most simple photovoltaic system, let alone 
> one with a 300 amp CT service and 400 amp transfer switch, is installed 
> correctly.  I know in the 1980s the solar water heating industry had acquired 
> a collective black-eye due to shoddy installation procedures and I fear this 
> is where the PV industry may be headed. 
>  
> I submitted a handful of photos and was granted a final approval.  I have 
> very mixed feelings about this “success.”  I feel like I cheated on a test. 
>  
> I am curious if any of you have had a similar experience to this.  As always 
> I am informed and sometimes amused by what I learn on this forum.
>  
> List of requested photographs:
>  
> ☐ PV module model number, quantity, and location according to the approved 
> plan. 
> ☐ Roof penetrations flashed/sealed according to the approved plan. 
> ☐ Array exposed cables are properly secured, supported, and routed to prevent 
> physical damage. 
> ☐ Grounding/bonding of rack and modules according to the manufacturer’s 
> installation instructions. 
> ☐ Equipment installed, listed and labeled according to the approved plan 
> (e.g., PV   modules, dc/dc converters, combiners, inverters, rapid shutdown 
> equipment). 
> ☐ Overcurrent devices are the type and size according to the approved plan. 
> ☐ Disconnects according to the approved plan and properly located as required 
> by the  NEC. 
> ☐ PV system markings, labels and signs according to the approved plan. 
> ☐ Connection of the PV system to the grounding electrode system according to 
> the approved plan. 
> ☐ Access and working space for operation and maintenance of PV equipment such 
> as  inverters, disconnecting means and panelboards (not required for PV 
> modules) [NEC 110.26]. 
> ☐ The rapid shutdown system is installed and operational according to the 
> approved  plan [NEC 690.12].
>  
>  
> William Miller
>  
> Miller Solar
> 17395 Oak Road, Atascadero, CA 93422
> 805-438-5600
> www.millersolar.com
> CA Lic. 773985
>  
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to