I’ve got offgrid  2 clients and they have no issues. 

They each have a Bolt and can choose the charging rate. They can run it at 
either power. But only use higher power when they have lots of sun. 
Older Stacked vfx and Schneider xw, no issues. 

I would expect the SW to work, however it’s an odd beast as it’s waveform steps 
change with load. More load, more steps, therefor cleaner so maybe at lower 
charge rate it’s not clean enough. 

As to your issue it could be power factor Being really poor. 
Can you tell us what inverter, yea 5 years ago is a long time. 



Jay

Peltz power. 





> On Jun 7, 2020, at 11:53 AM, Darryl Thayer <darylsol...@gmail.com> wrote:
> 
> 
> I think you said it well, about 5 years ago I tried to charge a car from an 
> off-grid system.  I did not record my events but the inverter had twice the 
> power of the level two charger, yet the inverter would get hot and trip out.  
> I was told a ferroresonant transformer may help, and it might be different 
> with different cars.  However, I was warned the ferroresonant was to stop 
> input wave problems from arriving at the output not to prevent the output 
> wave problems showing up on the input.   The off-grid customer gave up.
> 
>> On Sun, Jun 7, 2020 at 6:36 AM Hilton Dier III <hiltond...@gmail.com> wrote:
>> The issue with EV chargers is that they create a lot of reactive power. 
>> Think of it as "slosh" in the waveform. That means that charging at 2,000 
>> watts sloshes a lot more than 2kW through the cable, plug, outlet, and from 
>> the inverter. If you've got a reasonably good sinewave inverter the charger 
>> will like it fine. However, the inverter might not like the charger if you 
>> cut things too close. Make sure to have a lot of top end left in your 
>> inverter. Always use a transformer based inverter. The SW series has a big 
>> chunk of metal in it, so that's good. At 120V the Bolt will only draw 1440 
>> watts max.
>> 
>> An aftermarket Bolt 240V charger can draw up to 32 amps. That's 7.7 kW, so 
>> too big for an SW. Treat it more like 40 amps. The OEM 120/240 EVSE (smart 
>> charging cord) that comes with the car can draw 8 or 12 amps at 120V or 12 
>> at 240V. Assume that the 8 amps is really 12 and the 12 is really 15 or a 
>> bit more. I have seen 15 amp plugs and outlets with the hot prong melting 
>> plastic around it. The plug on the OEM EVSE is 20A rated but make sure your 
>> outlet is as well.
>> 
>> -- 
>> Hilton Dier III
>> Missisquoi River Hydro
>> Renewable Energy Design
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to