> On Mar 22, 2020, at 4:04 PM, Jay <jay.pe...@gmail.com> wrote:
> 
> 
> Ray, 
> Have you heard bought about using the Aux relay to control the AC output at 
> what ever voltage you want?
> 
> Jay
> 
> 
> 
> 
>>> On Mar 22, 2020, at 3:13 PM, Ray <r...@solarray.com> wrote:
>>> 
>> 
>> That's the whole point: we need the LBCO to be higher than 48v to catch the 
>> beginning of that steep drop off, so that there is still enough reserve left 
>> to keep the monitoring and solar charge controllers in operation, and avoid 
>> the dreaded dark start.  With Simpliphi, we don't have the dark start, but 
>> it still requires manual reset.   This isn't theoretical, we have been 
>> having serious trouble with a system because of Schneider's inability to set 
>> the LVD above 48 v.  Also setting the voltage higher (lower DOD) extends the 
>> cycle life of these batteries.  Otherwise, I love the stable 51 volts of 
>> Li+, even under load.  
>> 
>> Ray Walters
>> Remote Solar
>> 303 505-8760
>>> On 3/22/20 4:15 PM, Jerry Shafer wrote:
>>> Wrenches
>>> Don't let the LBCU scare you as this battery has such a flat SOC line that 
>>> when it falls off there is not much left in the tank. In addition set the 
>>> flex net to low SOC at 15% and critical to 10%.
>>> 
>>> On Sun, Mar 22, 2020, 12:15 PM Sindelar Solar <al...@sindelarsolar.com> 
>>> wrote:
>>>> Specifically with Blue Ion, the installation manual recommends 48V as 
>>>> LBCO, but also recommends setting it a bit higher:
>>>> 
>>>> "Recommended Low Voltage Disconnect Setting: 48 VDC (~2-10% State of 
>>>> Charge)
>>>> BMU will power down the Blue Ion 2.0 cabinet at 44 VDC (<1% State of 
>>>> Charge)
>>>> Based on system discharge patterns, SoC and voltage correlations will vary.
>>>> We recommend you err on the side of caution with a higher LVD setting and 
>>>> adjust as necessary.
>>>> To prevent a dark start event, we recommend leaving a little reserve “fuel 
>>>> in the tank”."
>>>> 
>>>> I have used 48VDC with success, and had one system indeed shut down at 
>>>> 44V, leaving 1% left to reboot.
>>>> 
>>>> Allan
>>>> 
>>>>> On 3/22/2020 12:44 PM, Ray wrote:
>>>>> Blue Ion, and Simpliphi that I know of.
>>>>> 
>>>>> Ray Walters
>>>>> Remote Solar
>>>>> 303 505-8760
>>>>> On 3/21/20 2:48 PM, Dave Angelini Offgrid Solar wrote:
>>>>>> I see what you mean Ray. Sorry I misread your mail. There are not too 
>>>>>> many batteries out there that need LBCO above 48V. Which ones are you 
>>>>>> talking about please?
>>>>>> 
>>>>>> Dave Angelini Offgrid Solar
>>>>>> 
>>>>>> "we go where powerlines don't"
>>>>>> http://members.sti.net/offgridsolar/
>>>>>> e-mail  offgridso...@sti.net
>>>>>> text 209 813 0060
>>>>>>> On Sat, 21 Mar 2020 11:18:21 -0700, Dave Angelini Offgrid Solar 
>>>>>>> <offgridso...@sti.net> wrote:
>>>>>>> 
>>>>>>> Hi Ray,
>>>>>>> 
>>>>>>> Which XW? There are 3 now. The old graybox XW defaults at 44V LBCO and 
>>>>>>> the range is 40 to 48V. There also was firmware back in its day that 
>>>>>>> got older units updated. Schneider still has the firmware under 
>>>>>>> discontinued products.
>>>>>>> 
>>>>>>> XW+ is default 44V and adjustable 36 to 44 vdc.
>>>>>>> 
>>>>>>> XW pro is running downstairs and I will take a look. It would be my 
>>>>>>> guess that it is the same as XW+. I think one needs to be sure they are 
>>>>>>> in Advanced settings to tweak LBCO also.
>>>>>>> 
>>>>>>> I am not plugging Schneider and have done work for both Outback and 
>>>>>>> Schneider as well as my clients. Hope this helps. 
>>>>>>> 
>>>>>>> Dave Angelini Offgrid Solar
>>>>>>> "we go where powerlines don't"
>>>>>>> http://members.sti.net/offgridsolar/
>>>>>>> e-mail  offgridso...@sti.net
>>>>>>> text 209 813 0060
>>>>>>> On Sat, 21 Mar 2020 11:46:21 -0400, Ray <r...@solarray.com> wrote:
>>>>>>> 
>>>>>>> We've been having good luck with SImpliphi, the pricing has recently 
>>>>>>> gotten much more competitive.  As it's names states, its simple.  Each 
>>>>>>> 3.8 kWh unit has an 80 amp breaker built into the top, weigh about 75 
>>>>>>> lbs, and are a bit smaller than an L16 but with carry handles.  We use 
>>>>>>> an insulated 2 pole combiner block to run all the parallel conductors 
>>>>>>> to the main 2/0 cable.  No monitoring, but they do have an handy setup 
>>>>>>> guide with recommended settings, specific for each manufacturer 
>>>>>>> (including Outback). 
>>>>>>> 
>>>>>>> Note to all:  Schneider XW can still not set its LVD above 48, which 
>>>>>>> basically makes it incompatible with most Li+ batteries.  Their tech 
>>>>>>> support has been abysmal as well.   We're looking forward to them as 
>>>>>>> one of the larger companies in the business, to put additional 
>>>>>>> resources into their engineering, and come out with at least a firmware 
>>>>>>> update to correct this problem.  
>>>>>>> 
>>>>>>> Ray Walters
>>>>>>> Remote Solar
>>>>>>> 303 505-8760
>>>>>>> On 3/20/20 3:59 PM, David Katz wrote:
>>>>>>> Hello Wrenches,
>>>>>>> I am working with some people that want to use a 20 kw-hour to 30 
>>>>>>> kw-hour 48 volt lithium-ion battery with an Outback Radian and Outback 
>>>>>>> FM charge controllers.
>>>>>>> They are considering using Discover, Blue-Ion, Battle Born or SimpliPhi 
>>>>>>> batteries.
>>>>>>> Does any one have any recommendations of which battery functions best 
>>>>>>> with the Outback system.
>>>>>>> Thanks,
>>>>>>> David Katz
>>>>>>> 
>>>>>>> 
>>>>>>> _______________________________________________
>>>>>>> List sponsored by Redwood Alliance
>>>>>>> 
>>>>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>>>>> 
>>>>>>> Change listserver email address & settings:
>>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>> 
>>>>>>> List-Archive: 
>>>>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>>>> 
>>>>>>> List rules & etiquette:
>>>>>>> www.re-wrenches.org/etiquette.htm
>>>>>>> 
>>>>>>> Check out or update participant bios:
>>>>>>> www.members.re-wrenches.org
>>>>>>> 
>>>>>> 
>>>>>> 
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>> 
>>>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>>>> 
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>> 
>>>>>> List-Archive: 
>>>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>>> 
>>>>>> List rules & etiquette:
>>>>>> www.re-wrenches.org/etiquette.htm
>>>>>> 
>>>>>> Check out or update participant bios:
>>>>>> www.members.re-wrenches.org
>>>>>> 
>>>>> 
>>>>> 
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>> 
>>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>>> 
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>> 
>>>>> List-Archive: 
>>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>> 
>>>>> List rules & etiquette:
>>>>> www.re-wrenches.org/etiquette.htm
>>>>> 
>>>>> Check out or update participant bios:
>>>>> www.members.re-wrenches.org
>>>>> 
>>>> -- 
>>>> Allan Sindelar
>>>> al...@sindelarsolar.com
>>>> NABCEP Certified PV Installation Professional
>>>> New Mexico EE98J Journeyman Electrician
>>>> Founder (Retired), Positive Energy, Inc.
>>>> 505 780-2738 cell
>>>> 
>>>>  
>>>> 
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> 
>>>> List-Archive: 
>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>> 
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>>> 
>>> 
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org