Wrenches
Don't let the LBCU scare you as this battery has such a flat SOC line that
when it falls off there is not much left in the tank. In addition set the
flex net to low SOC at 15% and critical to 10%.

On Sun, Mar 22, 2020, 12:15 PM Sindelar Solar <al...@sindelarsolar.com>
wrote:

> Specifically with Blue Ion, the installation manual recommends 48V as
> LBCO, but also recommends setting it a bit higher:
>
> "Recommended Low Voltage Disconnect Setting: 48 VDC (~2-10% State of
> Charge)
> BMU will power down the Blue Ion 2.0 cabinet at 44 VDC (<1% State of
> Charge)
> Based on system discharge patterns, SoC and voltage correlations will vary.
> We recommend you err on the side of caution with a higher LVD setting and
> adjust as necessary.
> To prevent a dark start event, we recommend leaving a little reserve “fuel
> in the tank”."
>
> I have used 48VDC with success, and had one system indeed shut down at
> 44V, leaving 1% left to reboot.
>
> Allan
> On 3/22/2020 12:44 PM, Ray wrote:
>
> Blue Ion, and Simpliphi that I know of.
>
> Ray Walters
> Remote Solar
> 303 505-8760
>
> On 3/21/20 2:48 PM, Dave Angelini Offgrid Solar wrote:
>
> I see what you mean Ray. Sorry I misread your mail. There are not too many
> batteries out there that need LBCO above 48V. Which ones are you talking
> about please?
>
> *Dave Angelini Offgrid Solar*
>
> *"we go where powerlines don't"
> http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/>
> e-mail  offgridso...@sti.net <offgridso...@sti.net>
> text 209 813 0060*
>
> On Sat, 21 Mar 2020 11:18:21 -0700, Dave Angelini Offgrid Solar
> <offgridso...@sti.net> <offgridso...@sti.net> wrote:
>
> Hi Ray,
>
> Which XW? There are 3 now. The old graybox XW defaults at 44V LBCO and the
> range is 40 to 48V. There also was firmware back in its day that got older
> units updated. Schneider still has the firmware under discontinued products.
>
> XW+ is default 44V and adjustable 36 to 44 vdc.
>
> XW pro is running downstairs and I will take a look. It would be my guess
> that it is the same as XW+. I think one needs to be sure they are in
> Advanced settings to tweak LBCO also.
>
> I am not plugging Schneider and have done work for both Outback and
> Schneider as well as my clients. Hope this helps.
>
> *Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/>
> e-mail  offgridso...@sti.net <offgridso...@sti.net>
> text 209 813 0060*
>
> On Sat, 21 Mar 2020 11:46:21 -0400, Ray <r...@solarray.com>
> <r...@solarray.com> wrote:
>
> We've been having good luck with SImpliphi, the pricing has recently
> gotten much more competitive.  As it's names states, its simple.  Each 3.8
> kWh unit has an 80 amp breaker built into the top, weigh about 75 lbs, and
> are a bit smaller than an L16 but with carry handles.  We use an insulated
> 2 pole combiner block to run all the parallel conductors to the main 2/0
> cable.  No monitoring, but they do have an handy setup guide with
> recommended settings, specific for each manufacturer (including Outback).
>
> Note to all:  Schneider XW can still not set its LVD above 48, which
> basically makes it incompatible with most Li+ batteries.  Their tech
> support has been abysmal as well.   We're looking forward to them as one of
> the larger companies in the business, to put additional resources into
> their engineering, and come out with at least a firmware update to correct
> this problem.
>
> Ray Walters
> Remote Solar
> 303 505-8760
>
> On 3/20/20 3:59 PM, David Katz wrote:
>
> Hello Wrenches,
> I am working with some people that want to use a 20 kw-hour to 30 kw-hour
> 48 volt lithium-ion battery with an Outback Radian and Outback FM charge
> controllers.
> They are considering using Discover, Blue-Ion, Battle Born or SimpliPhi
> batteries.
> Does any one have any recommendations of which battery functions best with
> the Outback system.
> Thanks,
> David Katz
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
> --
>
> *Allan Sindelar*
> al...@sindelarsolar.com
> NABCEP Certified PV Installation Professional
> New Mexico EE98J Journeyman Electrician
> Founder (Retired), Positive Energy, Inc.
> *505 780-2738 cell*
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to