Wes – Indeed, max Sunny Island 240VAC cluster is 4 units, so 23kW max BATTERY 
power.

Limit of roughly 27kW of PV (4x 120V x 56A relay limit = 26,880W) with that 
cluster if grid-tied with backfeed, so around 50kW max daytime load offset per 
cluster.  That may help if peak loads are always daytime?

Are you trying to take these systems off-grid, or just reduce peak load?

Best regards –
Mike

SMA America
Michael Mahon
Technical Trainer, Solar Academy
6020 West Oaks Boulevard, Suite 300
Rocklin, CA 95765
U.S.A.
Mobile:   +1 916 918 9412
www.SMA-America.com<http://www.sma-america.com/>

Solar Academy: https://solaracademy.sma.de/en.html

SMA America Solar Academy webinars: https://solaracademy.sma.de/en/courses.html
Choose "United States"

[cid:image001.jpg@01D5E8C5.9D7E9E60]<http://www.facebook.com/pages/SMA-America/140290312717395>[cid:image002.jpg@01D5E8C5.9D7E9E60]<http://twitter.com/SMA_America>
 [cid:image003.jpg@01D5E8C5.9D7E9E60] <http://www.smainverted.com/>  [Linkedin 
Logo] <http://www.linkedin.com/company/364675>  
[cid:image005.jpg@01D5E8C5.9D7E9E60] 
<http://www.youtube.com/playlist?list=PL840A5336CAC32332>  [SMAAFORUM_ICON] 
<http://smaadvance.com/signup/>
[cid:image007.jpg@01D5E8C5.9D7E9E60]<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.sma-america.com%2Fpowerup%2Finstaller.html&data=02%7C01%7CMichael.Mahon%40sma-america.com%7C19488d9c48b84303ddbc08d77e8cd1c6%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637117015597965454&sdata=wEbm4oer7wM5j7RZzXN5khOa99j6%2F57m4uCqbDtG6DA%3D&reserved=0>

This email and any attachments thereto may contain SMA America, LLC 
confidential, privileged and private material for the sole use of the intended 
recipient. Any review, copying, or distribution of this email (or any 
attachments thereto) by others is strictly prohibited. If you are not the 
intended recipient, please contact the sender immediately and permanently 
delete the original and any copies of this email and any attachments thereto. 
Thank you.

From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of wes 
kennedy
Sent: Friday, February 21, 2020 2:38 PM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>; Jeff Clearwater 
<je...@villagepowerdesign.com>
Subject: Re: [RE-wrenches] High Power Split phase inverter/chargers

Hi Jeff,

I think the biggest split phase sunny island system is 4 units, so that's 24KW.

What do you do for larger systems? Segment the loads? Not always very practical.

This latest opportunity is for an agricultural building that peaks at 75KW.



-Wes Kennedy 303-653-3073


On Friday, February 21, 2020, 12:47:39 PM MST, Jeff Clearwater 
<je...@villagepowerdesign.com<mailto:je...@villagepowerdesign.com>> wrote:


All of my SMA Sunny Island Sunny Boy AC coupled systems greater than 12 KW have 
worked flawlessly and delivered reliable power and good monitoring for years.  
Less excited about my Schneider and Outback systems due to callbacks and 
hassles.  a bit more expensive but worth it IMHO.

Hope that helps!

Jeff

wes kennedy wrote on 2/21/20 9:41 AM:

Hi friends,

I keep running across opportunities with 50KW-300KW peak load requirements, on 
split phase services. Big homes, agriculture etc.

Outback, Schneider, SMA can all gang/stack into the 30-50KW range, but north of 
there, I am not finding many (any?) options?

Just found Aims Power 50 KW split phase unit with claims of higher power 
offerings by special order. Even the 50KW unit is $20K, so quite spendy. Any 
experience with these guys?
50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384 Vdc TO 
220/230/240 
Vac<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.aimscorp.net%2F50kw-50-000-watt-dc-to-ac-pure-sine-power-inverter-charger-384-vdc.html&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C9b17a515fc3c4935965f08d7b7168f75%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C1%7C637179179837002896&sdata=2%2BQrNJCOqR6CbgWIW30VGBJFECsuEa9eMVs%2BLfCL8sM%3D&reserved=0>

50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384 Vdc TO ...

50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384 Vdc Split 
Phase 220/230/240


Thanks for any input!

-Wes Kennedy 303-653-3073
on this list since the 90's



_______________________________________________

List sponsored by Redwood Alliance



List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>



Change listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C9b17a515fc3c4935965f08d7b7168f75%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C1%7C637179179837022884&sdata=d3rrO%2FwsF2xOk%2Fc06mXlGWGKgZAwNcePIETQtMnENow%3D&reserved=0>



List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C9b17a515fc3c4935965f08d7b7168f75%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C1%7C637179179837022884&sdata=X0%2B6Fwf2kfy4fm1tkdFzjBRvmXuNzccqGzMh2fhFc0s%3D&reserved=0>



List rules & etiquette:

www.re-wrenches.org/etiquette.htm<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C9b17a515fc3c4935965f08d7b7168f75%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C1%7C637179179837032883&sdata=X%2Fac4TAtXrcziGf0jhnsMOvi6LCuBzulNBatL35FzGA%3D&reserved=0>



Check out or update participant bios:

www.members.re-wrenches.org<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.members.re-wrenches.org%2F&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C9b17a515fc3c4935965f08d7b7168f75%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C1%7C637179179837042877&sdata=7sMFSSQL9yLltgJJheiB3gv1387rXuk3zgE0xffXzak%3D&reserved=0>



--
~~~~~~~~~~~
Jeff Clearwater
Village Power Design
linkedin<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Fjeff-clearwater-0622a312%2F&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C9b17a515fc3c4935965f08d7b7168f75%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C1%7C637179179837042877&sdata=vVXspAJKFh4P5yqpvb3YuPCkG%2FE1Nmv9ckCQo0C7nd8%3D&reserved=0>
www.villagepowerdesign.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.villagepowerdesign.com%2F&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C9b17a515fc3c4935965f08d7b7168f75%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C1%7C637179179837052871&sdata=XITcRREVH50tMPuiSoRUAQYC73Ue1fKOy82wa%2Fny%2Bcc%3D&reserved=0>
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to