Hello Bruce,

If the CSW is unable to maintain 210V L1 to L2 it will display this fault F01.

  1.  Measure DC voltage at the inverter terminals, ensure DC is within range.
  2.  With AC breaker open, check inside wiring compartment for output voltage
  3.  If F01 is present with AC breakers open, the damage is internal to the 
inverter

Also, I would like to understand your comment about tech support not taking 
your call.
Could you please contact me directly?

Thanks
Sandra Herrera
425-210-0163
sandra.herr...@se.com


From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of 
br...@willpowerelect.com
Sent: Thursday, August 22, 2019 6:15 PM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] SW fault code low output voltage


[External email: Use caution with links and attachments]

________________________________


Group,

I'm not very familiar with Schneider equipment, but would like to understand 
fault code 00F1 on a CSW 4024.
Low voltage output. Any remedy? Have reset several times but fault continues. 
Inverter only two years old.
Tech support wouldn't take my call 'cause I'm not on their 'certified' list.

Thanks!

Bruce Fiero


P: 541.535.3965
F: 541.512.0061
E: br...@willpowerelect.com<mailto:br...@willpowerelect.com>
W: Willpower Electric, 
LLC<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.willpower-electric.com&data=02%7C01%7Csandra.herrera%40se.com%7C3654fe0b13be40268d9a08d727676b10%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637021197437689828&sdata=FIJ6FxPrL3f51jKSWjOYclQ9RzkYjdnqrUoKBV1NS1Y%3D&reserved=0>


CCB 191852
Oregon Electrical Contractor C681
NABCEP Certified Solar (PV) Installer 031409-38

DUNS 191470363
Energy Trust of Oregon Trade Ally Solar (PV) Installation & Energy Efficient 
Commercial Lighting Programs



______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to