Hi William,

Yes, the bulletin I attached was just an example of a 100% rated disconnect
(which happened to be DC since that's the one I had handy!).  My
understanding is that most of the NON-fused Square D switches are rated for
100%.

See this FAQ from the manufacturer:
https://www.schneider-electric.us/en/faqs/FA237949/, quoted below:


> *Resolution:*All General Duty, Heavy Duty or Double Throw Safety Switches
> maximum current rating, either 80% or 100% of the nameplate rating, depends
> on if the switch is Fusible or NON-Fusible.
>
>    - Fusible switches are rated to carry up to 80% of the amp rating of
>    the fuses installed in the switch
>
>
>    - Non-fusible (unfused) switches are rated to carry 100% of the switch
>    nameplate ampere rating
>
>
 Regarding this point:

> If, hypothetically, you could find a 30A disconnect that was continuous
> duty rated, if it is fed by a 40 Amp breaker, as I believe would be
> required, then the 30 Amp disconnect is still not suitable.  You can not
> feed a 30 Amp rated device with more than 30 Amps.


I believe the original poster was asking about a 6000W inverter with 25A
max output.  So in that case you could use a 100% rated non-fusible
disconnect, because the max current is only 25A.  (The required 40A breaker
is sized larger because commonly available breakers are only 80% rated, not
100%.  But the max current is still only 25A.)  See 690.8(A) for
calculation of maximum circuit current, specifically section (3) for
inverters: "The maximum current shall be the inverter continuous output
current rating."  (Not "the inverter continuous output current multiplied
by 1.25.")

Best,
Blake

On Wed, Aug 21, 2019 at 10:59 PM William Miller <will...@millersolar.com>
wrote:

> Blake:
>
>
>
> Thanks for sharing the data sheet.  The document applies to DC PV systems,
> however, and I believe the discussion pertains to the AC inverter output.
> Therefore the bulletin you attached does not apply here.
>
>
>
> (Note also that this data sheet indicates you need to use two poles for
> any application, ungrounded or grounded.  I believe that requirement was
> usurped later on for Square D Heavy Duty switches, but again, that is for a
> different application.)
>
>
>
> I looked again at Square D general and heavy duty safety switches rated at
> 30 Amps and I could not find any reference that these switches are
> continuous duty rated.  I still believe that for the application described,
> the 125% rating has to be applied.
>
>
>
> If, hypothetically, you could find a 30A disconnect that was continuous
> duty rated, if it is fed by a 40 Amp breaker, as I believe would be
> required, then the 30 Amp disconnect is still not suitable.  You can not
> feed a 30 Amp rated device with more than 30 Amps.
>
>
>
> Bottom line, a 30 Amp disconnect will not meet code on the described
> project.
>
>
>
> William Miller
>
>
>
>
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
> Quote of the month:  “As they age, batteries transition from energy
>
> storage devices to energy consuming devices.“ W. Miller
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Blake Gleason
> *Sent:* Wednesday, August 21, 2019 4:20 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] 30 amp disconnect/40 amp breaker
>
>
>
> Typically a fused disconnect can only handle 80% of it's nominal current
> on a continuous basis.  Unfused disconnects are often 100% rated.  For
> example, see attached Square D bulletin #3110DB0401R0410.
>
>
>
> So, a 100% rated (unfused) 30A disconnect (at least, from Square D) should
> be fine here, as long as your OCPD is provided elsewhere (eg, the breaker
> you mentioned).
>
>
>
> NEC 690.8(B)(1)(Exception) explicitly allows a 100%-rated device to be
> used without multiplying the inverter output current by 125%.
>
>
>
>
>
> On Wed, Aug 21, 2019 at 3:22 PM Greg <g...@remotepowerinc.com> wrote:
>
> Fellow Wrenches,  I'm having a discussion with a utility engineer
> regarding the following situation:
>
> Installing a 6kW inverter that has a full rated output of 25 amps.  80% of
> 30 is 24.  That means to me I need to go up to a 40 amp breaker.  I'm
> running #8 (continuous load 25 x 1.25 etc.)
> The engineer believes I should use a 60 amp disco since it's on a 40 amp
> breaker.  My thinking is I can use a 30 amp disco since it can not produce
> more than 25 amps ever.
>
> Do any of you have a reference that shows what I'm doing is okay? Not
> okay?
>
> Thanks again,
> Greg Egan
> Remote Power Inc.
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
>
> --
>
>
>
>
>
> *Blake Gleason, PE* | Employee-Owner |
>
> *Director of Innovation & Technical Excellence*
>
>
> 510.845.2997 x128
>
> Follow us on Facebook
> <https://www.facebook.com/pages/Sun-Light-Power/119675658118322?ref=hl>,
> LinkedIn <https://www.linkedin.com/company/sun-light-and-power> or our
> website <https://sunlightandpower.com/>.
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 


*Blake Gleason, PE* | Employee-Owner |


*Director of Innovation & Technical Excellence*


510.845.2997 x128

Follow us on Facebook
<https://www.facebook.com/pages/Sun-Light-Power/119675658118322?ref=hl>,
LinkedIn <https://www.linkedin.com/company/sun-light-and-power> or our
website <https://sunlightandpower.com/>.
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to