Hi Wrenches,

I've got an issue that I'm remotely trying to troubleshoot but I must be
missing something.
Specs:
Off-grid
Dual Outback FXR 3648s recently installed
FM100, with about 4k of solar
2 x 16 kWh Blue Ion Batteries, installed this past week
Kohler 14 generator
Outback Mate 3s

The issue is that the FXR inverters aren't charging the batteries when the
generator is running, they are just passing the power through to the
loads.  I have verified that AC Input is in "Use" not "Drop" when generator
is running, I have disabled all of the advanced charging (ie Global charge,
float coordination, auto-charge termination and auto grid-tie control) .  I
have told it to "start bulk" both remotely and through the owner on site.
I have done a reboot multiple times of the whole system as well as the Mate
3s.  I even had the owner try a factory reset and firmware update on the
Mate 3s.  The firmware was successfully updated and it appears the factory
reset on the mate.

Nothing has changed how it behaves with the generator, generator just
follows the load and no AC charging takes place.  Oddly, this was working
fine when we left, we had topped the batteries off with the generator.

Any ideas what I might be missing?

Thanks for your suggestions
-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to