I'm surprised I did not get more of a response on this thread. Is anyone
else adding onto M series microinverter systems? I'm starting to get a lot
of requests to add more panels to older microinverter systems. Using the IQ
combiner seems to make a lot of sense. The existing M series Envoy can just
be plugged in nearby. I really like this approach but I don't want to run
into a situation where I find out does not allow for this.

On Thu, Jun 6, 2019, 2:34 PM Jason Szumlanski <
ja...@floridasolardesigngroup.com> wrote:

> Yes, correct. The M Series Envoy would be plugged in elsewhere, close to
> the IQ Combiner.
>
> The situation is that a customer already has a combo system installed by
> some clown with all wrong wire sizes, OCPD, disconnects, and
> interconnection on the load side of a whole house generator. It's a mess
> and I'm starting over. I literally had to remove ALL of the panels and
> mounts for a re-roof because it was done so poorly and the roof is leaking
> now. Anyway, the cleanest way to combine all the circuits is to bring all 4
> circuits in one conduit into an IQ Combiner and just use that combine into
> one supply-side connection with a fusible disconnect. The M Series neutrals
> can just pass through the IQ Combiner (plus one for the IQ Envoy). It would
> supply the required OCPD protection. I guess my main concern is whether
> this device is listed for use only as an IQ system combiner only or if the
> individual components are listed, which would allow this setup for sure I
> would imagine.
>
> Jason
>
>
>
>
> On Thu, Jun 6, 2019 at 11:54 AM Chad Waits <chadwa...@netzerosolar.net>
> wrote:
>
>> Only thing I see is you will have to have 2 Envoys. The IQ inverters send
>> the data on the powered conductors, not on the neutral like the M250’s.
>>
>> Chad Waits
>> President/Owner – Net Zero Solar
>> 101 W. 5th St., Tucson, AZ  85705
>> Office: 520-207-4053
>> Cell: 520-270-4873
>> NABCEP Certified PV Installation Professional
>>
>>
>>
>> From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> on behalf
>> of Jason Szumlanski <ja...@floridasolardesigngroup.com>
>> Reply-To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
>> Date: Thursday, June 6, 2019 at 8:42 AM
>> To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
>> Subject: [RE-wrenches] Enphase IQ combiner for M series microinverters
>>
>> Does anyone see anything wrong with using an Enphase IQ combiner to
>> combine two strings of IQ microinverters with two strings of M250
>> microinverters? I would not use the production CT (just use microinverter
>> production data).
>>
>> I can't see any technical reason this can't be done. Do any listing or
>> code reasons come to mind?
>>
>> Jason Szumlanski
>> Florida Solar Design Group
>> _______________________________________________ List sponsored by Redwood
>> Alliance List Address: RE-wrenches@lists.re-wrenches.org Change
>> listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or
>> update participant bios: www.members.re-wrenches.org
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to