Louis:

Thanks for the message. I’m a bit embarrassed that I misunderstood the start 
voltage significance. I modified the string wiring and system is operating. 
Thanks again!

William Miller

> On Apr 24, 2019, at 7:46 AM, <lo...@solarcowboyz.com> 
> <lo...@solarcowboyz.com> wrote:
> 
> William,
> 
> The start voltage is 285v from what I see covered on the specifications in 
> manual.
> Data sheets are not specifications, I have seen many a error on these over 
> the years.
> 
> This voltage is way low regardless if the start voltage was 220v.
> By the time the PV voltage gets dragged down when finding the VMPP it is 
> going to be down near the low end of the range anyway.
> 
> I always like to see the VMPP up near the top of the VMPP point(but not to 
> high!).
> This means less current, which means less heat, which means longer life.
> 
> Looks like the is either a PV problem or a bad design in the first place.
> 
> Louis Segarra
> 
> 
> -------- Original Message --------
> Subject: Re: [RE-wrenches] SMA Micro-grid
> From: William Miller <will...@millersolar.com>
> Date: Tue, April 23, 2019 11:40 am
> To: Harry Mahon <michael.ma...@sma-america.com>
> Cc: RE-wrenches <re-wrenches@lists.re-wrenches.org>
> 
> Mike:
> 
> Thanks for the reply. Good information. 
> 
> The AC system is 208. The data sheet indicates that for 208 the PV startup is 
> 220. Today we have 260 VDC. That should be enough!?
> 
> I checked EMT he AC frequency in case it was on shift mode. It is right at 
> 60.00. 
> 
> Still in waiting mode. I had always thought “waiting” was for grid reconnect 
> timeout...
> 
> William
> 
>> On Apr 23, 2019, at 8:47 AM, Harry Mahon <michael.ma...@sma-america.com> 
>> wrote:
>> 
>> William –
>> Waiting mode means the DC voltage is below the inverter start.  For SB 
>> 4000-12, that would be 285 VDC (and will work to 250VDC once that is hit).
>>  
>> If you knock on the inverter lid, the display will cycle and you will see 
>> the DC voltage displayed.
>>  
>> If the yellow LED is not on, this should not be an AC side issue.
>>  
>> I do not think the “Backup Mode” parameter would be the cause, but if the 
>> voltage check shows well above PVstart, it would be worth a call to service. 
>>  If the inverter was left in on grid mode, then it will work when the SI is 
>> creating a micro-grid with frequency within UL1741 limits.  If the system is 
>> off-grid, I would think the SB would have been set to off-grid mode rather 
>> than enabling Backup Mode to “on all” that allows switching from on-grid to 
>> off-grid parameter sets by RS485 command.
>>  
>> Best-
>> Mike
>>  
>> From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of 
>> William Miller
>> Sent: Monday, April 22, 2019 6:54 PM
>> To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
>> Subject: [RE-wrenches] SMA Micro-grid
>>  
>> Friends:
>>  
>> I am working on an AC coupled SMA system in an off-grid setting.  We have an 
>> SB4000-12 that was disconnected for a number of years and we reconnected it. 
>>  The inverter is stuck in the waiting mode and  will not generate power.  
>> The Sunny Islands and Sunny Boys are connected via an RS485 communication 
>> system.
>>  
>> I suspect there is a programming step I have not yet accomplished.  I recall 
>> some years ago I programmed the other Sunny Boys for off-grid operation.  I 
>> can’t find anything in any of the manuals about how to check the 
>> programming.  I also suspect SAM tech support talked me through this and the 
>> information may not be published.
>>  
>> Does this ring a bell with any of you?  Any advice? 
>>  
>> Thanks in advance.
>>  
>> William Miller
>>  
>> Miller Solar
>> 17395 Oak Road, Atascadero, CA 93422
>> 805-438-5600
>> www.millersolar.com
>> CA Lic. 773985
>>  
>> Quote of the day:  “If there is a job you hate, get really,
>> really good at it. Maybe you will hate it less.“ W. Miller
>>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to