William - yes, waiting is usually waiting for grid to come back within spec or for DC voltage to get to start. 260 should be plenty. 208V with neutral should be fine without adjusting the jumpers. Have you measured the AC voltage at the inverter terminals?
May want to contact service for this one. 1-877-697-6283. Best regards – Mike From: William Miller <will...@millersolar.com> Sent: Tuesday, April 23, 2019 12:40 PM To: Harry Mahon <michael.ma...@sma-america.com> Cc: RE-wrenches <re-wrenches@lists.re-wrenches.org> Subject: Re: [RE-wrenches] SMA Micro-grid Mike: Thanks for the reply. Good information. The AC system is 208. The data sheet indicates that for 208 the PV startup is 220. Today we have 260 VDC. That should be enough!? I checked EMT he AC frequency in case it was on shift mode. It is right at 60.00. Still in waiting mode. I had always thought “waiting” was for grid reconnect timeout... William On Apr 23, 2019, at 8:47 AM, Harry Mahon <michael.ma...@sma-america.com<mailto:michael.ma...@sma-america.com>> wrote: William – Waiting mode means the DC voltage is below the inverter start. For SB 4000-12, that would be 285 VDC (and will work to 250VDC once that is hit). If you knock on the inverter lid, the display will cycle and you will see the DC voltage displayed. If the yellow LED is not on, this should not be an AC side issue. I do not think the “Backup Mode” parameter would be the cause, but if the voltage check shows well above PVstart, it would be worth a call to service. If the inverter was left in on grid mode, then it will work when the SI is creating a micro-grid with frequency within UL1741 limits. If the system is off-grid, I would think the SB would have been set to off-grid mode rather than enabling Backup Mode to “on all” that allows switching from on-grid to off-grid parameter sets by RS485 command. Best- Mike From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>> On Behalf Of William Miller Sent: Monday, April 22, 2019 6:54 PM To: RE-wrenches <re-wrenches@lists.re-wrenches.org<mailto:re-wrenches@lists.re-wrenches.org>> Subject: [RE-wrenches] SMA Micro-grid Friends: I am working on an AC coupled SMA system in an off-grid setting. We have an SB4000-12 that was disconnected for a number of years and we reconnected it. The inverter is stuck in the waiting mode and will not generate power. The Sunny Islands and Sunny Boys are connected via an RS485 communication system. I suspect there is a programming step I have not yet accomplished. I recall some years ago I programmed the other Sunny Boys for off-grid operation. I can’t find anything in any of the manuals about how to check the programming. I also suspect SAM tech support talked me through this and the information may not be published. Does this ring a bell with any of you? Any advice? Thanks in advance. William Miller Miller Solar 17395 Oak Road, Atascadero, CA 93422 805-438-5600 www.millersolar.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.millersolar.com%2F&data=02%7C01%7CMichael.Mahon%40sma-america.com%7C814937113e444889a87208d6c81b26b0%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C636916416278614333&sdata=ccnu0LEvaiSaHYhls5v3ClRB4xQMDA8jpy5RIevjkcs%3D&reserved=0> CA Lic. 773985 Quote of the day: “If there is a job you hate, get really, really good at it. Maybe you will hate it less.“ W. Miller
_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org