Have you checked their voltage calibration against your DMM?Chris Worcester 
[email protected] 530-448-9692on my Samsung Galaxy S7.
-------- Original message --------From: Darryl Thayer <[email protected]> 
Date: 3/25/19  2:05 PM  (GMT-08:00) To: newrewrenches 
<[email protected]> Subject: Re: [RE-wrenches] Xantrex XW6048 
(quad) blowing past setpoints Is the chargingfrom the inverter orfrom a solar 
source?On Mon, Mar 25, 2019, 3:35 PM Jason Szumlanski 
<[email protected]> wrote:I have four inverter/chargers (master 
and 3 slaves) that are blowing past their 57.6V setpoint that I programmed and 
confirmed via the Context Combox. They are hitting 58.4V and tripping the 
battery management units on a set of Lithium Batts. Any ideas why this would 
happen? I can disable chargers on individual units, so I know the settings are 
getting uploaded via the Combox. Jason Szumlanski
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to