That is a strange panel.  If you are feeding a breaker panel yes you must
be farther from the line connections to the bus bar, unless the busbars are
limited in the total load breakers in which case the other set of rules
apply.  How and what you connect depends upon the service at that point.
 If it is delta not wye, as you said, you have to use a true 480-volt
inverter, not a 277-480 inverter.  The difference is the ground
connection-neutral bond.  The 480 Delta could be grounded as corner ground
making the legs 480, 480, 0 volts, or as a center tap 240-480-volt making
the legs 240, 240, 415 volts to ground.  If however, it is not a delta but
a wye the legs would all be 277-volts to ground.    Be sure to check
voltages and with your inverter supplier so you have the correct
configuration.    20% of 600 A at 480-volt 3-phase is about 100 kW.  (600 x
0.2 x 480 x 1.73 = 99.600 Watts)
This system will have another transformer, either single phase or 3-phase
giving the 120-volt plug loads.

On Mon, Nov 5, 2018 at 9:04 AM frenergy <frene...@psln.com> wrote:

> Hey folks,
>
>              I've been asked to inter-tie a system to a 600 amp 480V
> delta panel.  Do all the same rules apply (Backfeed max 20%, keep
> inter-tie breaker farthest from panel grid feeders, anything else??).
> Proposed system size is about 35-40KW.  Its actually a bazillionaire's
> residence.
>
> TIA
>
> Bill
>
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049
> www.frenergy.net
>
>
> ---
> This email has been checked for viruses by Avast antivirus software.
> https://www.avast.com/antivirus
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to