Wrenches,

I recall seeing some past threads about SMA arc fault issues but am
curious if others are using SMA -40 inverters extensively and NOT seeing
intermittent arc faults?  If so, I would be curious what your DC
installation practices look like?  Are you ensuring that homerun ends use
connectors identical to your module manufacturer?  Are you crimping any DC
transitions? Perhaps using insulated lugs for DC transitions? What type of
conduit are you using for DC wiring? Are you using ferrules where you
terminate in the inverter?  Any other tips or suggestions are also
welcome.

At the moment arc faults for the SMA -40 inverters seem to be our main
service ticket at this time (surpassing Enphase replacements and
surpassing prior-model SMA arc fault issues).  The arc fault errors are
particularly prevalent on systems with Tigo optimizers installed though we
have occurrences on pretty much every -40 unit.  System meantime between
failure seems to be unpredictable but somewhere between 2-180 days.  There
does seem to be some correlation between systems with shading and Tigos
and prevalence of arc faults.  Shutting off arc fault seems to be the only
true solution which is obviously undesirable.

SMA has us update firmware and has had us shutoff Optitrac neither of
which resolve the issue.  They also ask us to check wiring connections
which almost never yields results (though we have found a squirrel or two
which makes one grateful that the arc fault function exists).

Thanks for any advice,

Matt




Matthew Partymiller
Solar Energy Solutions LLC
(877) 312-7456
m...@solar-energy-solutions.com


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to