Yep same here the ubiquitous CH361 and a midnite SPD and a Delta. I very
rarely need more than 2 strings so fuses and not used. I would never want
600v floating around in any enclosure with other electrical code or not! I
know grid -tie does this all the time but not for offgrid. IMHO.

There are a few other choices I have had to use I can dig up if needed. PM
me.

Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridso...@sti.net
text 209 813 0060

> Hi Howie,
>
> I have installed about 10 of these and all have worked well, longest
> operating unit about 3 years old. My only complaint is the 600V input
> breakers are not really thought through, as my understanding is code does
> not permit 600VDC within the PDP, Midnite, etc enclosure. So we use a
> SquareD CH361 external fused disconnect and keep all the 600V wiring
> external to the PDP. Curious how others approach that.
>
> Kevin Pegg
> EA Energy Alternatives Ltd.
> 37471 Hwy 16 E
> Telkwa, BC  V0J 2X2
> 250-846-9888
> Http://www.EnergyAlternatives.ca
>
>
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
> Behalf Of Howie Michaelson
> Sent: January-18-18 8:35 AM
> To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
> Subject: [RE-wrenches] Schneider 600volt Charge Controller
>
> Hi All,
> Anyone have feedback/review of the 600 volt Schneider Charge Controller
> that they'd care to share?  I have an existing Conext XW+ off-grid system
> with combox communication setup which currently has about 1.5 kW of solar
> feeding through 2 MX60s (no hub). We'll be adding about 5kW (on a TPM
> about 150' away) and I'm trying to decide if overall it would be better to
> use the Schneider 600v (which I haven't used before, although I have
> serviced the 150v XW with no real complaints).  Typically I would use a
> Classic200, but given the ability to integrate with the XW6848 and
> communicate through the Combox for more offsite visibility, I'm
> considering the Schneider, but only if it's not going to provide me with
> the benefit of added service calls.
> TIA!
> Howie
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridso...@sti.net
text 209 813 0060

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to