Thanks Nick!
So we will need two Envoys, which is what I expected.
My question # 5 again. Will the Enlighten software monitoring portal
aggregate all 64 Enphase micros into a single unified production view,
or will two separate production views (48 existing M215s; 16 new IQ6s)
be required for the same site?
Best regards,
Gary Willett PE
Icarus Engineering / Solar Services LLC
Irving TX
On 11/28/17 8:30 PM, Nick Soleil wrote:
Enphase does allow an IQ Envoy and an older Envoy (Envoy-S or earlier) on the
same site. We were initially conservative and didn't officially recommend
it, but have removed that wording from our IQ Microinverter datasheet and from
our trainings.
The new IQ Envoy won't talk to the M and S-series micros (and vice-versa), so
you will need two Envoys, one of them being an IQ Envoy.
Cordially,
Nick Soleil
Enphase Energy | Product Manager, Envoy and IQ Accessories
(707) 763-4784 x7267 // office
(707) 321-2937 // cell
[Enphase_esig_logo6.jpg]<https://enphase.com/>
Energy Evolved<http://enphase.com>™
Powering What’s Next™ | The Enphase Energy Management System<http://ow.ly/HbVS3>
NABCEP Certified Solar PV Installer #03262011-300
California C10 Licensed Electrician #986315
Texas Master Electrician #284451
________________________________
From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> on behalf of Jason
Szumlanski <ja...@floridasolardesigngroup.com>
Sent: Tuesday, November 28, 2017 4:49 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] MIXING ENPHASE M-2XX / IQ6 MICROS & ENVOY / IQ-ENVOY
ON SAME AC COMBINER LOAD CENTER
Although Enphase recommends against it I believe (mixing generations at
this time), in theory you need one ACCP, two Envoys (one of each type), and
you can aggregate into a single portal system (just add the second Envoy to
the activation). I think the mixing of systems is not recommended due to
potential communication interference.
From what I understand they are launching an IQ Envoy that will handle both
systems in the future, but they are not there yet.
I'm actually sourcing some M250's at this moment to add to a M215 system
for a client. I wanted to avoid the whole IQ issue and let someone else be
the guinea pig, so let us know what results you have! :)
We are about to have hundreds of homes with a mix of some with M series and
some with IQ series in very close proximity. This should be interesting!
But I don't expect any major issues home to home. The first IQ systems are
not showing any issues yet.
Jason Szumlanski
On Mon, Nov 27, 2017 at 8:27 PM, Gary Willett <g...@icarussolarservices.com>
wrote:
ESTEEMED WRENCHES:
I'm in the process of engineering a project to add 16 new Enphase IQ6
micros to an existing 48 Enphase M215-IG system that has been
in-service about 2 years.
The original system has a NEMA-3R outdoor AC Combiner Panel (ACCP) with
each of the (3) M215 AC strings landing on a separate 2-pole 20A
circuit breaker.
The Enlighten Envoy is mounted in a NEMA-4 plastic enclosure below the
ACCP, and is powered by a 1-pole 15A breaker in the ACCP.
My intent is to land the new 16-IQ6 string on a new 20A breaker in the
ACCP, and to power its Envoy (if needed) also from the ACCP.
In studying Enphase documents:
(A) IQ6 micros have to be monitored by an IQ-Envoy.
(B) Envoy uses a 1-pole "L1, "N", and "EGC" a dedicated NEMA-5R
receptacle branch circuit for power supply and its AC comms modem.
(C) IQ-Envoy uses "L1, "L2, and "N", for power supply and its AC
comms modem, and is wired directly to its dedicated 2-pole breaker.
My questions:
1. Can I replace the existing Envoy with a new IQ-Envoy, and monitor
the all 64 micros (48 existing M215s; 16 new IQ6s) with the new
IQ-Envoy?
2. If the answer to "1" is yes, that's what I would like to do.
3. If the answer to "1" is no, can I still land the new IQ6 string
on the existing ACCP, or do I need to place another ACCP just for
the new IQ6 string and any future growth?
4. If the answer to "1" is no, can the existing Envoy and the new
IQ-Envoy both be powered from the same ACCP?
5. If both the existing Envoy and the new IQ-Envoy can co-exist at
the same customer site, will the Enlighten software monitoring
portal aggregate all 64 Enphase micros into a single unified
production view, or will two separate production views be required?
Thanks for your help!
Gary Willett PE
Icarus Engineering / Solar Services LLC
Irving TX
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
<https://mailtrack.io/trace/link/2d50e8d87317466f2604245c61148c13af5cc414?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=161b5623c16b2865>
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
org/maillist.html
<https://mailtrack.io/trace/link/b8a84a64125069221e3e48e116f5ad05801cc108?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=030d43d59a94d35b>
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
<https://mailtrack.io/trace/link/86bec64039d1bb115d11bc42873dacff577a5ec4?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f74c76c512dc25db>
Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
<https://mailtrack.io/trace/link/7b88e6ec3c56f7b53523ca6c284c14755dcb3bdf?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=7f1e004f60256ca4>
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org