A 120/240 V split phase system is supplied by a
center tapped 240 V transformer. The center tap
is grounded, deriving the neutral. Unbalanced
current from the two hot phase conductors return back through the neutral.


At 08:27 PM 11/25/2016, you wrote:
Wrenches,
Is there such a thing as a "grid neutral"? I
have been providing design support to a client
for a large off grid system; a prepper, rare in
these parts. He claims that utility current is
carried in part through the ground and in part
through a neutral conductor, and such a "utility
neutral" is deliberately undersized. At first I
pushed back (see below). Now I just wonder what
Wrenches more knowledgeable than I am will say.
Thank you,
Allan

Allan Sindelar
<mailto:al...@sindelarsolar.com>al...@sindelarsolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
505 780-2738 cell

-------- Forwarded Message --------
Date: Thu, 24 Nov 2016 11:25:36 -0700

Allan
Happy thanksgiving. Sorry for the slow reply; overwhelmed here.

All wet sorry. If you look at the power lines
you will see two or three wires at top of pole
and the one smaller one a little ways down the
pole. This is the power station neutral.

The hots bidirectional is an explanation that
helps people understand current but is not totally clear.
Even if you use that visualization in order for
the electrons on the hot to oscillate they heed
a path to oscillate into and out of
That is the “neutral”.

Bottom line is from the power station and in
your home you have at least one hot and one neutral.
You can actually use the hot to light up a lite
bulb by connecting the other side of the lite bulb to the earth.
This one way you can get electrocuted.
I touched the hot side of a 220 circuit and the
current went thru me and into the earth…not much fun.

This has been openly publicly discussed and one
of the electrical association advised the power
companies to increase the size of the neutral to
solve many issues, such as cows giving less milk
and problems with electric current in homes. The
power companies even openly discuss this.

In remote rural areas of Australia, I have seen
electricity distribution using SWER (Single-Wire
Earth Return); just one wire is fed to the
property at a high voltage, with the current
returning via the ground.  At the property, a
transformer turns the high voltage into normal
residential voltages on a pair of wires (230VAC
in Australia vs 2x115V in some other countries).
But this SWER system is inefficient, and the
supply voltage is poorly regulated; it is a rare
exception - it is only done because of the high
cost of delivering two wires in remote areas.

In metropolitan areas, you will typically see 4
wires passing down the street. This consists of
three phases of "Active", plus a "Neutral". You
could imagine the Active carrying current "from"
the power grid, and the Neutral carrying the
current "back to" the power grid (even though the current flow is symmetrical).

There is lots of info online if you wish to learn more about this.
Take care, Robert

From: Allan Sindelar
[<mailto:al...@sindelarsolar.com>mailto:al...@sindelarsolar.com]
Sent: Sunday, October 23, 2016 10:18 PM

Robert,
I'm neither an electrical engineer or a utility
employee, so I may be all wet here, and if so
please dry me off with a straight-up
explanation. But this whole argument seems
specious to me, as it addresses a "grid neutral".

My reasoning is this - there is no such animal
as a "grid neutral" in utility lines, so how is
this issue even relevant? The "hots" are
bidirectional; only when the utility power is
stepped down at the transformer at the home is a
reference neutral created. To say that the
current "cannot all go back thru the neutral
since it is not large enough BY DESIGN" seems to
me an absurd concept since there is no neutral in utility power distribution.

Am I missing something?
Allan

On 10/2/2016 7:51 PM, Robert wrote:
Allan
Here is the info I said I would send:
<https://www.youtube.com/watch?v=aJOB2FIqUiQ>https://www.youtube.com/watch?v=aJOB2FIqUiQ.
Listen about 20 minutes at least.

All current that goes “out” on the two
residential or three commercial hots goes back on the grid neutral
AND thru the ground'. It cannot all go back thru
the neutral since it is not large enough  BY
DESIGN. So…. That means we really don’t have a clean ground anymore.

Thank you for your time today. It is enjoyable to speak with you.

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to