hi Allan,

One fact that might be useful to consider is that a three phase supply has 3 
hot/live/active wires and one neutral.  The 3 currents returning to the neutral 
actually cancel each other out (due to phase differences) and in a perfectly 
balanced load situation there is no need for a neutral, but where a number of 
diverse circuits are connected there will be some imbalance, so you need a wire 
there, but it need not be as heavy as the 3 “hot" ones.

cheers
Hugh

Hugh Piggott
Scoraig Wind Electric
Dundonnell
Ross shire
IV23 2RE,  UK
+44 77 1315 7600
h...@scoraigwind.co.uk
www.scoraigwind.co.uk <http://www.scoraigwind.co.uk/>



> On 26 Nov 2016, at 01:27, Allan Sindelar <al...@sindelarsolar.com> wrote:
> 
> Wrenches,
> Is there such a thing as a "grid neutral"? I have been providing design 
> support to a client for a large off grid system; a prepper, rare in these 
> parts. He claims that utility current is carried in part through the ground 
> and in part through a neutral conductor, and such a "utility neutral" is 
> deliberately undersized. At first I pushed back (see below). Now I just 
> wonder what Wrenches more knowledgeable than I am will say.
> Thank you,
> Allan
> 
> Allan Sindelar
> al...@sindelarsolar.com <mailto:al...@sindelarsolar.com>
> NABCEP Certified PV Installation Professional
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder (Retired), Positive Energy, Inc.
> 505 780-2738 cell
> 
> -------- Forwarded Message --------
> Date: Thu, 24 Nov 2016 11:25:36 -0700
> 
> Allan
> Happy thanksgiving. Sorry for the slow reply; overwhelmed here.
>  
> All wet sorry. If you look at the power lines you will see two or three wires 
> at top of pole and the one smaller one a little ways down the pole. This is 
> the power station neutral.
>  
> The hots bidirectional is an explanation that helps people understand current 
> but is not totally clear.
> Even if you use that visualization in order for the electrons on the hot to 
> oscillate they heed a path to oscillate into and out of
> That is the “neutral”. 
>  
> Bottom line is from the power station and in your home you have at least one 
> hot and one neutral.
> You can actually use the hot to light up a lite bulb by connecting the other 
> side of the lite bulb to the earth.
> This one way you can get electrocuted.
> I touched the hot side of a 220 circuit and the current went thru me and into 
> the earth…not much fun.
>  
> This has been openly publicly discussed and one of the electrical association 
> advised the power companies to increase the size of the neutral to solve many 
> issues, such as cows giving less milk and problems with electric current in 
> homes. The power companies even openly discuss this.
>  
> In remote rural areas of Australia, I have seen electricity distribution 
> using SWER (Single-Wire Earth Return); just one wire is fed to the property 
> at a high voltage, with the current returning via the ground.  At the 
> property, a transformer turns the high voltage into normal residential 
> voltages on a pair of wires (230VAC in Australia vs 2x115V in some other 
> countries). But this SWER system is inefficient, and the supply voltage is 
> poorly regulated; it is a rare exception - it is only done because of the 
> high cost of delivering two wires in remote areas.
>  
> In metropolitan areas, you will typically see 4 wires passing down the 
> street. This consists of three phases of "Active", plus a "Neutral". You 
> could imagine the Active carrying current "from" the power grid, and the 
> Neutral carrying the current "back to" the power grid (even though the 
> current flow is symmetrical).
>  
> There is lots of info online if you wish to learn more about this.
> Take care, Robert
>  
> From: Allan Sindelar [mailto:al...@sindelarsolar.com 
> <mailto:al...@sindelarsolar.com>] 
> Sent: Sunday, October 23, 2016 10:18 PM
>  
> Robert,
> I'm neither an electrical engineer or a utility employee, so I may be all wet 
> here, and if so please dry me off with a straight-up explanation. But this 
> whole argument seems specious to me, as it addresses a "grid neutral". 
> 
> My reasoning is this - there is no such animal as a "grid neutral" in utility 
> lines, so how is this issue even relevant? The "hots" are bidirectional; only 
> when the utility power is stepped down at the transformer at the home is a 
> reference neutral created. To say that the current "cannot all go back thru 
> the neutral since it is not large enough BY DESIGN" seems to me an absurd 
> concept since there is no neutral in utility power distribution. 
> 
> Am I missing something?
> Allan
> 
> On 10/2/2016 7:51 PM, Robert wrote:
> Allan
> Here is the info I said I would send: 
> https://www.youtube.com/watch?v=aJOB2FIqUiQ 
> <https://www.youtube.com/watch?v=aJOB2FIqUiQ>. Listen about 20 minutes at 
> least.
>  
> All current that goes “out” on the two residential or three commercial hots 
> goes back on the grid neutral 
> AND thru the ground'. It cannot all go back thru the neutral since it is not 
> large enough  BY DESIGN. So…. That means we really don’t have a clean ground 
> anymore.
>  
> Thank you for your time today. It is enjoyable to speak with you.
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org 
> <mailto:RE-wrenches@lists.re-wrenches.org>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
> <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to