I'm experimenting with a panel I built myself that is series'ed and
paralleled to produce a Voc of ~3.3 volts and ~10-12 amps which can be
alligator clipped to slacker 2V cells, leads running outside to a sunny
locale. It's certainly not the quickest/best solution but worth a try
in some instances and doesn't burn up many gallons of fuel cooking an
entire pack to save a couple slackers. Its pretty easy to find PV cells
and the rest of it to make your own...and it was kinda fun.
Bill
On 12/17/2015 3:59 AM, Chris Mason wrote:
I have a customer that has had AGM batteries in the Caribbean for many
years without any sign of capacity loss, but...they air condition (?)
the room they are in, and they do not use any discharge, they are
purely setup as a UPS style system. Unless the power fails, all the
power is exported, and they use grid power.
When using AGM as an offgrid solar system, they last about three years
here.
On Wed, Dec 16, 2015 at 9:44 PM, jay <jay.pe...@gmail.com
<mailto:jay.pe...@gmail.com>> wrote:
HI Luke,
Without knowing what the charging parameters its really hard to
know whats going on.
And this false issue with life span is years really gets me.
Batteries are measured in cycle life, period, So to say a IND
battery will get 15 to 20 years is bunk.
It’ll get the cycles based on DOD, if its charged correctly,
watered and the sun is in a good phase and, and and,
I’ve got a guy who’s worn out his Hup’s in around 5-6 years.
But how would any other but an IND battery worked with that hard
of a life, yikes, L-16’s would have been a set a year.
But I’m guessing his 11 year old batteries could be quite done.
And he is caught in the perfect bind.
Do you spend money on replacing some of the cells?
If it was my client, I’d say no, he’d be throwing good money after
bad.
jay
peltz power
> On Dec 16, 2015, at 12:50 PM, Dana <d...@solarwork.com
<mailto:d...@solarwork.com>> wrote:
>
> We recommend an EQ when there is a 0.02 SG differential on any
one cell to the rest of the pack, use a refractometer for SG
readings, install watering systems with a electrolyte port or
water the battery bank ourselves, & do not do systems without a
charging power backup.
>
>
----------------------------------------------------------------------------
> Dana Orzel
> Great Solar Works, Inc - NABCEP # 051112-136
> E - d...@solarwork.com <mailto:d...@solarwork.com> - Web -
solarwork.com <http://solarwork.com>
> O - 970.626.5253 <tel:970.626.5253> C - 208.721.7003
<tel:208.721.7003>
> "Responsible Technologies for Responsible People since 1988"
> Please consider the environment before printing this email.
>
>
>
> -----Original Message-----
> From: RE-wrenches
[mailto:re-wrenches-boun...@lists.re-wrenches.org
<mailto:re-wrenches-boun...@lists.re-wrenches.org>] On Behalf Of Dave
> Sent: Wednesday, December 16, 2015 10:23 AM
> To: 'RE-wrenches'
> Subject: Re: [RE-wrenches] HuP Conundrum
>
> Luke,
>
> Contac HUP for specific advice. You've probably already done that?
>
> What comes to mind:
> Since you have two series strings, run the house on one string
of all good cells.
>
> Pull out the weak cells and charge them as per HUP's advice.
>
> I'm guessing that this problem has happened because the
homeowner did not properly charge the batteries.
> Homeowner most likely did not use a hydrometer upon EQ'ng the cells.
> Homeowner thought the cells were fully charged and equal but
obviously they were not.
> Record keeping, log books etc.. for people caring for expensive
batteries are well worth the effort.
>
> David Palumbo
> Independent Power LLC
> 462 Solar Way Drive
> Hyde Park, VT 05655
> 802-371-8678 <tel:802-371-8678> cell
> 802-888-4917 <tel:802-888-4917> home
>
>
>
>
>
> -----Original Message-----
> From: RE-wrenches
[mailto:re-wrenches-boun...@lists.re-wrenches.org
<mailto:re-wrenches-boun...@lists.re-wrenches.org>] On
> Behalf Of Luke Christy
> Sent: Wednesday, December 16, 2015 12:01 PM
> To: RE-wrenches
> Subject: [RE-wrenches] HuP Conundrum
>
> Hi Friends,
>
> With all of the battery threads going on right now I figured it
would be a
> good time to start another one.
>
> I have a customer with a large off-grid system who has just
started having
> trouble with a bank of HuP batteries. This system is 48V with 8x 12V
> 6-85F-27S batteries in two series strings. Charging is supplied
by around 10
> kW of PV.
>
> I didn't install the system and the customer has always taken
care of the
> maintenance and watering himself. He has seemingly been pretty
diligent
> about taking care of things, including equalizing on a regular
basis.
> However, recently he started having voltage problems and when I
made a site
> visit to check on the batteries, I found that 3 of the 8x 12V
batteries each
> had a cell with SG so low it wouldn't register on my hydrometer.
>
> Obviously this is a problem, and owing to some complicating
factors I'm not
> really sure how best to address the issue.
>
> Replacing the entire battery bank will be unbelievably
expensive, especially
> given that the house is in a remote location and there is
difficult access
> to the battery room. To add a another factor, the house is currently
> unoccupied while the owner tries to sell the property, so he is
not exactly
> eager to invest a lot of money into battery replacement.
>
> The batteries are only 11 years old, so they should
theoretically have quite
> a bit of life left in them. Perhaps those of you with more
experience with
> larger batteries can advise. Can the cells be resurrected with
careful
> charging and equalizing?
>
> What would you do?
>
> Thanks as always for opinions and advice.
>
> Luke Christy
>
> NABCEP Certified PV Installation ProfessionalT: Certification
#031409-25
> NABCEP Certified Solar Heating InstallerT: Certification
#ST032611-03
>
>
> Solar Gain Services, LLC
> PO Box 531
> Monte Vista, CO. 81144
> sgsrenewab...@gmail.com
> 719.588.3044 <tel:719.588.3044>
> www.sgsrenewables.com <http://www.sgsrenewables.com>
>
>
>
>
>
>
>
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
--
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician
www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org