Jarmo,

I must say I disagree with most of what you have said. In the EV DIY industry, 
there are a growing number of conversions using LFP battery banks without any 
BMS or EMS at all. These pioneers are risking there multi-thousand banks 
because they have learned something about these cells. They will stay in 
balance and perform perfectly as long as they prevent over and under voltage or 
charging a frozen battery with high current. 

My reply numbers correlate to yours:
I agree for most customers a BMS is necessary.
Disagree: The battery systems (with BMS) that I sell do not regulate cell 
voltages during charge or discharge. They only adjust voltage after the cells 
reach 3.55 Vpc. However, at that 3.55 Vpc, I have terminated charge and entered 
a float/maintenance charge. On my personal battery bank, 24 cells, I have 
charged and discharged daily since May. My cell voltages still only vary by 
0.02 volts per cell.
Disagree: There is no temperature adjustment for voltage during charge or 
discharge. All temperature compensation circuits are removed from the RE 
equipment per manufacturers specifications.
Disagree: We provide a continuous float voltage per manufacturer 
specifications. A float voltage can keep the battery at any SoC. I program for 
90%.
Our CPU provides protection for over current BUT that will likely never happen 
because the cells can be charged and discharged up to 10C and continuously at 
3C!
Disagree: No need to limit inverter current as the battery can produce 10C.
Disagree: Ditto above.
Disagree: No need to limit inverter charge current because of the 10C 
capability.
I agree that for most consumers a BMS is required. So far we install the BMS 
provided by the manufacturer on every system. I will be installing systems 
without BMS in the future but openly for select customers.

I have not found that LFP batteries are “amazingly sensitive”. I have 
discharged cells past 100% DoD, in fact as low as 0.35 Vpc, and recharged 
without any harm. I have started very complex loads like air conditioners with 
repeatable success from small battery banks. While I do not recommend this, I 
believe there is a robustness with modern LFP cells. 

The benefits of LFP batteries are many. Each year I recycle between 30,000 and 
40,000 pounds of lead acid batteries. MOST of them are damaged by the consumer 
deficit charging them. I consider this to be a very unfavorable aspect of lead 
acid when compared to LFP batteries that never need to be fully charged or 
equalized or watered.

One thing that will damage LFP batteries is if a cell in a series string is 
ever discharged below 0 volts, it will take on reverse polarity and is usually 
not recoverable. But, you can simple replace it and balance it with the other 
cells. 

I welcome your comments.

Respectfully yours,

Larry Crutcher


On Sep 15, 2014, at 8:08 PM, jarmo.venalai...@schneider-electric.com wrote:

Hi: 

We've done some testing and operation of Lion battery banks in the 10 kWh range 
with our inverter chargers and so far the most important findings are: 

1. The battery pack must have its own battery management system to: 
a. regulate the individual cell voltages during charge and discharge 
b. balance the cell voltages during charge and discharge 
c. adjust cell charging voltages due to temperature variations 
d. not provide a continuous float voltage to the battery bank 
d. provide a built in safety cutoff disconnect, which turns off the current if 
for any reason either the charge or discharge current is too high. 

A series string of Lion cells, without the battery management system functions 
above is very likely to result in damaged cells or worse.  The most likely 
mechanism which ultimately causes damage is individual cell temperature or cell 
to cell voltage imbalance. 

2. The inverter system must be designed so that the inverter never draws so 
much current that the current limit circuit in the battery bank is triggered. 

3. It may be necessary to adjust the current limit circuit as they typically 
respond within milli-seconds and may be triggered on simple power up as the 
inverter cap bank charges up. 

4. When working with Lion, the inverter/charger should be configured so that it 
is a simple current limited voltage source when in charge mode.  The built in 
battery management system should take care of the required charge cycle 
operation. 

5. Whether the pack is LiFePO4, Lion polymer or other does not appear to be as 
important as a having a reputable brand and more importantly a well designed 
built in battery management system. 

The short version is that lead acid cells are amazingly forgiving with regards 
charging and discharging voltages, currents and temperatures.  Lion cells on 
the other hand are amazingly sensitive and going out of bounds on any of these 
can and will cause irreparable damage.   

Given the sensitivity, it doesn't make sense to take on responsibility for Lion 
battery management. 

Management of that sensitivity and responsibility is best left to the battery 
bank manufacturer. 

JARMO








_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to