Marco, here’s a scenario – a bit theoretical, but I’m curious to get your input 
since you’ve been active on this topic for a while (I’m assuming the values 
below are reasonably accurate – I haven’t looked at the datasheets for a while):



ABB 300’s

Enphase 215

Max Power

300

225

Max Current

1.25

.94

Inverters/Circuit

12

17

kW/Circuit (based on 270W modules)

3.24

4.59


If I have a 100A residential panel with a 100A main, I am limited to 
backfeeding a single 20A circuit or doing a supply side connection.  If I got 
1500kWh/kW with ABB and 1450 kWh/kW (3% energy loss due to clipping) with 
Enphase, would it be worth avoiding the supply side connection?  What if I get 
1472 kWh/kW?  Where would you draw the line.

Isaac Opalinsky | Technical Trainer | SunPower Corporation
Desk 443-569-3476 | Cell 443-277-6286

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Marco Mangelsdorf
Sent: Monday, August 25, 2014 11:11 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] Inverters Maximum Input Ratings

Look, guys, what’s beyond dispute is that when we size the solar array higher 
than the nameplate inverter output, there will be clipping that takes 
place….i.e., harvestable solar power that goes nowhere.  The higher that 
oversize percentage, the more clipping will take place.

If the design choice, as noted below, is to use a 270-watt module (from a 
manufacturer that learned last week that a recall notice was published by the 
U.S. Consumer Product Safety Commission 
https://www.cpsc.gov/en/Recalls/2014/SolarWorld-Recalls-Solar-Systems-with-Copper-Grounding-Lugs/
 ), does it make sense to use a micro inverter that has a max output of about 
225 watts (M215) or 250 watts (M250) when there are micros (e.g., ABB 300) that 
can handle the full output of the 270 which guarantees NO clipping?

marco

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Jerry Shafer
Sent: Monday, August 25, 2014 8:00 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Inverters Maximum Input Ratings


Why dont you use the m250 anyway as the 250's so far are more reliable then the 
215 have been. A little off topic i know.
On Aug 25, 2014 1:41 PM, "Jason Szumlanski" 
<ja...@fafcosolar.com<mailto:ja...@fafcosolar.com>> wrote:
I had a tough customer recently that grilled me on how we can put a 270W solar 
module on a 215W inverter. Fortunately, Enphase has a wonderful white paper on 
the subject. However, it got me thinking... Enphase has demonstrated that 
higher output panels in many climates (hot SW Florida included) can benefit 
from modules that far exceed the inverter rating, and even exceed the 
inverter's "recommended input" rating. Enphase has shown that 270W+ modules can 
show energy harvest on the M215 where it makes sense to "oversize" the module.

I also received a similar query from a rather uninformed plan reviewer in an 
area AHJ along similar lines. Fortunately I was within the "recommended input" 
rating on the spec sheet of 270W with a 265W module, but I wonder what would 
happen if I had paired the M215 with a 280W module on my plans, which are 
becoming readily available now in 60 cell modules with 300W modules on the near 
horizon. I'm pretty sure my plan would have been kicked back for exceeding the 
manufacturer's recommendation.

My question, which applies to string inverters and microinverters, is how much 
is too much, what would happen if you paired an array that far exceeded the 
rating, and how do inverter manufacturers determine the recommended and/or 
maximum rating of the connected module or array? Also, why do some 
manufacturers have a simple recommendation while others have a "maximum" rating?


Jason Szumlanski
​Fafco Solar​



_______________________________________________
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to