What am I missing here?

In the 2014 NEC, 705.21 seems to indicate that every inverter needs to have its 
own AC disconnect. Most inverters only have integrated DC disconnects (SMA, 
Power One, Fronius) as I recall. Or has this been interpreted to only apply to 
the DC side of the system?

 

Since NYS is still on the 2008 NEC, and the handbook has a note in 690.64B)1:

The outputs of utility-interactive inverters may not be connected directly in 
parallel without first being connected to the required dedicated circuit 
breaker or fusible disconnecting means.

 

Further, I believe it can be interpreted that each inverter source circuit 
connection “shall be made at a dedicated circuit breaker or fusible 
disconnecting means” as directly quoted from 690.64(B)1.

 

I see a dedicated OCPD being required for each inverter output, unless the 
manufacturer has installation instructions which have been approved by UL 
indicating that more than one can be paralleled and retain its listing (ala 
microinverters).

 

-Glenn

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Corey Shalanski
Sent: Monday, June 30, 2014 2:38 PM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Combining Multiple Inverters

 

Thank you to all who responded to this thread - particularly Jason/Dave/Jay for 
pointing out the maximum OCPD requirements.

 

Getting back to my original question.. I would like to use Dave's "extremely 
small subset" example of two SB5s operating at 277V. In this case, if we were 
to parallel the output of each inverter onto a 50A OCPD (#6 wire), could we 
downsize the wire to #10 from the split going back to each individual inverter? 
or would we be better served (required?) to run #6 all the way back to each 
unit? Since we are dealing with current-limited devices I would tend to think 
we can downsize but wanted to get Wrenches' feedback on this.

 

--

Corey Shalanski

Joule Energy

New Orleans, LA

  
<https://mailfoogae.appspot.com/t?sender=aY3NoYWxhbnNraUBqb3VsZS1lbmVyZ3kuY29t&type=zerocontent&guid=4bec5788-9903-4ff4-8f92-031ee1997a9c>
 ᐧ

 

On Fri, Jun 27, 2014 at 12:41 PM, <re-wrenches-requ...@lists.re-wrenches.org> 
wrote:


Message: 5
Date: Fri, 27 Jun 2014 11:32:02 -0400
From: Dave Click <davecl...@fsec.ucf.edu>
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Combining Multiple Inverters
Message-ID: <53ad8e72.4080...@fsec.ucf.edu>
Content-Type: text/plain; format=flowed; charset=ISO-8859-1

This is an interesting conversation, but I'm not sure it's going to
really impact anything.

When an inverter is listed, it is tested with some "maximum output
overcurrent protection" as part of its rating per UL 1741. Typically
inverter manufacturers set this to be just above the inverter's max
current + 25%. As you know, many inverters can work at more than one
voltage, so for the SB5s their max current ratings at 277/240/208V are
18/20.8/24A, respectively. The max overcurrent protection is 50A. This
figure often appears in the manual but not in the data sheet. For SMA,
it's in the manuals. For some manufacturers, it's only available from
tech support.

For the Sunny Boy line, the only way you could have more than one
inverter on a shared OCPD is if you have two SB5s operating at 277V
(18.1A rated current each, so 2x18.1x1.25 < 50A). The SB6, SB7, and SB8
all have currents too high to make this work, as they share the 50A max
OCPD. The SB3/3.8/4 have a max OCPD of 30A, which is too low to
double-up since each SB3 requires an OCPD of at least 20A. The TLs don't
work either, as the max for any unit is too low. I don't see it in the
SMA manual, but I know that in other manuals I've seen a manufacturer
requirement for a dedicated OCPD. The only inverters I know of that have
a max OCPD rating far beyond their rated current are micro-inverters.

As for the shared disconnect, since at least the 2005, 690.15 has noted,
"A single disconnecting means in accordance with 690.17 shall be
permitted for the combined ac output of one or more inverters or ac
modules in an interactive system." That being said, the NEC requires ac
modules and micro-inverters to have ac disconnects (connectors,
typically) per 690.6 and 690.15(A). 690.15 notes that an inverter be
able to be disconnected from all sources, but if doubling up these SB5s
you could argue that this shared disconnect accomplishes that via the
anti-islanding protection... so I agree now that this is a grey area.

Anyway, it comes down to whether it's worth worrying about this for what
is an extremely small subset of compatible inverter configurations, when
you can just do something like install a $50 Eaton BR24L70RP (70A bus,
240V, 4 spaces) with two 30A breakers and be on your way.

DKC

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to