When this subject came up, the first thing that I thought of was our
micro-inverter combiner that
takes 3 strings of many inverters, (each inverter W/OUT OCPD), but does
have an OCPD for each string.
That would have to be code compliant of course. (MNPV6 Disco combiner
Micro for example)
Enphase for instance can have something like 16 micro-inverters on one
string going
into the combiner using their cable.
boB
On 6/27/2014 8:32 AM, Dave Click wrote:
This is an interesting conversation, but I'm not sure it's going to
really impact anything.
When an inverter is listed, it is tested with some "maximum output
overcurrent protection" as part of its rating per UL 1741. Typically
inverter manufacturers set this to be just above the inverter's max
current + 25%. As you know, many inverters can work at more than one
voltage, so for the SB5s their max current ratings at 277/240/208V are
18/20.8/24A, respectively. The max overcurrent protection is 50A. This
figure often appears in the manual but not in the data sheet. For SMA,
it's in the manuals. For some manufacturers, it's only available from
tech support.
For the Sunny Boy line, the only way you could have more than one
inverter on a shared OCPD is if you have two SB5s operating at 277V
(18.1A rated current each, so 2x18.1x1.25 < 50A). The SB6, SB7, and
SB8 all have currents too high to make this work, as they share the
50A max OCPD. The SB3/3.8/4 have a max OCPD of 30A, which is too low
to double-up since each SB3 requires an OCPD of at least 20A. The TLs
don't work either, as the max for any unit is too low. I don't see it
in the SMA manual, but I know that in other manuals I've seen a
manufacturer requirement for a dedicated OCPD. The only inverters I
know of that have a max OCPD rating far beyond their rated current are
micro-inverters.
As for the shared disconnect, since at least the 2005, 690.15 has
noted, "A single disconnecting means in accordance with 690.17 shall
be permitted for the combined ac output of one or more inverters or ac
modules in an interactive system." That being said, the NEC requires
ac modules and micro-inverters to have ac disconnects (connectors,
typically) per 690.6 and 690.15(A). 690.15 notes that an inverter be
able to be disconnected from all sources, but if doubling up these
SB5s you could argue that this shared disconnect accomplishes that via
the anti-islanding protection... so I agree now that this is a grey area.
Anyway, it comes down to whether it's worth worrying about this for
what is an extremely small subset of compatible inverter
configurations, when you can just do something like install a $50
Eaton BR24L70RP (70A bus, 240V, 4 spaces) with two 30A breakers and be
on your way.
DKC
On 2014/6/27, 6:53, Richard L Ratico wrote:
I may be playing devil's advocate here, but I want to add a few
thoughts. Jay, I
just looked at Fronius and SMA inverter data sheets. I found no spec.
for an
output OCPD, only a spec for max. output current.
William, most inverters now come with integrated DC/AC discos. Dave,
2014 NEC
705.12(D)(1), IMHO, specifies ONE OCPD for the entire interconnected
power
system, not individual OCPD for each inverter.
Generally speaking OCPD is provided for the circuit conductors in a
system, not
the individual pieces of equipment. If the equipment manu. specifies
OCPD, that
is a different story.
I understand the 2014 code to require appropiate OCPD for all the
conductors
from the panelboard to the inverter. If that can be accomlished with
one device
at the panel, it meets code. That said, code is a MINIMUM standard.
Bottom line, I agree with Corey that there is no code requirement for
individual
OCPD for each inverter. If there is, unfortunately, it is insufficiently
explicit such that we are having this conversation.
Dick Ratico
Solarwind Electric
--- You wrote:
I have never seen an inverter that does not specify a OCPD size.
Jay
Peltz power.
Sent from my iPhone
On Jun 26, 2014, at 3:20 PM, Dave Click <davecl...@fsec.ucf.edu> wrote:
Corey,
The line of reasoning is faulty. It's 705.12(D)(1). Micro-inverters
are the
exception because they are specially listed to share a breaker. As
for the other
inverters, doubling them up on a single breaker / disconnect probably
goes
against their installation instructions [110.3(B)] and it's unlikely
that you
could put multiple units on a single breaker anyway because when you
take (2
inverters) x (rated current) x (1.25) you will probably come up with
a minimum
breaker size that is larger than the maximum allowed under the NRTL
listing to
UL 1741.
Dave
On 2014/6/26, 16:18, Corey Shalanski wrote:
We considered the necessity to shut down individual inverters and
determined
that the added costs of an inverter output combiner panel were not
merited. I
agree that in theory it seems beneficial to be able to switch each
inverter
individually, but how often does this occur in practice? For the
relatively
infrequent cases where we need to return to a jobsite and shut down
an inverter
- for troubleshooting/removal/etc. - we do not mind shutting down the
other
inverters (up to a limit) for what is hopefully a short period of time.
Again, this whole line of reasoning may be shown to be faulty if
someone can
directly point to the Code section that requires OCPD on each individual
inverter.
--
Corey
$E1eB
On Thu, Jun 26, 2014 at 9:20 AM,
<re-wrenches-requ...@lists.re-wrenches.org>
wrote:
Message: 5
Date: Wed, 25 Jun 2014 19:17:57 -0700
From: William Miller <will...@millersolar.com>
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Combining Multiple Inverters
Message-ID: <04f4b8fd-e280-4bf2-b5a4-c2fca8d1c...@millersolar.com>
Content-Type: text/plain; charset="utf-8"
Not allowed. You need a dedicated OCPD. Plus seems like a really
bad idea.
How do you shut down just one inverter?
Miller Solar
--- end of quote ---
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org