Then how do we install microinverters?  705.12(D)(1) says OCPD for each 
inverter is required at the point of interconnection with distribution 
equipment.  But as long as the conductors are sized to the OCPD, we follow the 
branch-circuit/feeder tap rules, and the inverter’s maximum OCPD limit is not 
exceeded, what is the issue?  I’m assuming the inverter’s maximum OCPD is 
usually the limiting factor, but I’ve been intrigued by the fact that the ABB 
TRIO has an option for AC OCPD in the inverter – it seems like there must be a 
cost-effective solution for tapping a trunk cable with a string inverter just 
as we do with microinverters.  Has anyone tried this?

Isaac Opalinsky | Technical Trainer | SunPower Corporation
Desk 443-569-3476 | Cell 443-277-6286

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Glenn Burt
Sent: Wednesday, June 25, 2014 10:19 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Combining Multiple Inverters

Code requires OCPD on the output of each inverter, so not sure where the 
savings would be..
________________________________
From: Corey Shalanski<mailto:cshalan...@joule-energy.com>
Sent: ‎6/‎25/‎2014 21:19
To: RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>
Subject: [RE-wrenches] Combining Multiple Inverters
I am curious about best practices for combining the output of multiple 
inverters:

  *   We are considering using an insulated tap "Polaris/Burndy" connector in 
lieu of a solar accumulation panel. We would then run the output of this tap 
connector through a fused disconnect and on to the interconnection. Does anyone 
else do this?
  *   In the above scenario, how should we size the wire between each 
inverter's output and the tap connector? Since there is no OCPD on this wire, 
would we have to use the same wire gauge as the combined output? or can we get 
away with sizing each wire according to its associated inverter output rating?
--
Corey Shalanski
Joule Energy
New Orleans, LA
[http://portal.mxlogic.com/images/transparent.gif]ᐧ
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to