Hi Jason,

Always good to get a different view on how to do it. 
I've always found it easier and cheaper to pull the circuits off the roof to 
the AC combiner, so my overcurrent is in a different location

Jay
Peltz power






> On Apr 30, 2014, at 5:08 AM, Jason Szumlanski <ja...@fafcosolar.com> wrote:
> 
> Each microinverter string needs dedicated overcurrent protection. If 
> combining strings on the roof for a single run back to the interconnection 
> point, you need each string to have it's own breaker/fuse. The other option 
> is to run each string back to the interconnection point separately, but for a 
> 10kW system you have to do a supply side connection anyway on as typical 200A 
> service, so combining strings somewhere is necessary, and a single run from 
> the roof makes sense in many cases.
> 
> 
> Jason Szumlanski 
> ​Fafco Solar​
>  
> 
> 
> 
>> On Tue, Apr 29, 2014 at 6:40 PM, jay peltz <j...@asis.com> wrote:
>> Follow up to Bill's point.
>> 
>> For Micros I've installed a disconnect on the roof, but never a breaker or 
>> fuse
>> Why install a breaker?
>> 
>> jay
>> 
>> peltz power
>> 
>>> On Apr 29, 2014, at 9:43 AM, Bill Hoffer wrote:
>>> 
>>> Dave
>>> 
>>> I agree, in the case of microinverters, you already have a main PV System 
>>> disconnect at the Load Panel to shut down the system that is readily 
>>> accesible.  I would consider the disconnect on the roof as a supplemental 
>>> disconnect for the purposes of maintenance by authorized personal that only 
>>> needs to be accessible.  
>>> 
>>> Bill
>>> 
>>> 
>>>> On Tue, Apr 29, 2014 at 8:44 AM, Dave Click <davecl...@fsec.ucf.edu> wrote:
>>>> I think 240.24(A)(4) allows the installation of the inverter OCPDs in the 
>>>> SolaDeck hidden under a module.
>>>> 
>>>> 240.24 Location in or on Premises.
>>>> (A) Accessibility. Overcurrent devices shall be readily accessible and 
>>>> shall be installed so that the center of the grip of the operating handle 
>>>> of the switch or circuit breaker, when in its highest position, is not 
>>>> more than 2.0 m (6 ft 7 in.) above the floor or working platform, unless 
>>>> one of the following applies:
>>>> ...
>>>> (4) For overcurrent devices adjacent to utilization equipment that they 
>>>> supply, access shall be permitted to be by portable means.
>>>> 
>>>> 
>>>> And if panelboards / fused safety switches are allowed to have 
>>>> screwed-down covers over the OCPDs, I'd think that installing a removable 
>>>> module over these OCPDs would meet NEC. I guess an AHJ could argue that 
>>>> this requires TWO covers be removed, unlike a panelboard or a switch.
>>>> 
>>>> DKC
>>>> 
>>>> 
>>>>> On 2014/4/29, 11:15, Jason Szumlanski wrote:
>>>>> 690.9(D) is not applicable to the original discussion because we were 
>>>>> talking about an Inverter output circuit, not a PV Source or Output 
>>>>> circuit.
>>>>> 
>>>>> 690.34 may apply if you call a SolaDeck with breakers a junction box, but 
>>>>> I can see that being a stretch in the mind of many. 
>>>>> 
>>>>> My and Ray's question about the screws on the SolaDeck cover itself 
>>>>> requiring a tool to render it accessible is still an issue if the 
>>>>> breakers themselves need to be "readily accessible," but that would also 
>>>>> apply to a Midnite MNPV, which also has a cover with a screw.
>>>>> 
>>>>> 
>>>>> Jason Szumlanski
>>>>> 
>>>>>> 
>>>>>>> On 4/28/2014 5:57 PM, Bill Brooks wrote:
>>>>>>> Read 690.9(D) and 690.34. Not sure where this “hysteria—run for the 
>>>>>>> border” sentiment is coming from.
>>>>>>> 
>>>>>>>  
>>>>>>> 690.9(D) Photovoltaic Source and Output Circuits. Listed PV
>>>>>>> 
>>>>>>> overcurrent devices shall be required to provide overcurrent
>>>>>>> 
>>>>>>> protection in PV source and output circuits. The overcurrent
>>>>>>> 
>>>>>>> devices shall be accessible but shall not be required to
>>>>>>> 
>>>>>>> be readily accessible.
>>>>>>> 
>>>>>>>  
>>>>>>> 690.34 Access to Boxes. Junction, pull, and outlet boxes
>>>>>>> 
>>>>>>> located behind modules or panels shall be so installed that
>>>>>>> 
>>>>>>> the wiring contained in them can be rendered accessible
>>>>>>> 
>>>>>>> directly or by displacement of a module(s) or panel(s) secured
>>>>>>> 
>>>>>>> by removable fasteners and connected by a flexible
>>>>>>> 
>>>>>>> wiring system.
>>>>>>> 
>>>>>>>  
>>>>>>> This is not a change. Please help me understand the concern.
>>>>>>> 
>>>>>>>  
>>>>>>> Bill Brooks.
>>>>>>> 
>>>>>>>  
>>>>>>>  
>>>>>>> From: re-wrenches-boun...@lists.re-wrenches.org 
>>>>>>> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray 
>>>>>>> Walters
>>>>>>> Sent: Monday, April 28, 2014 2:23 PM
>>>>>>> To: RE-wrenches
>>>>>>> Subject: Re: [RE-wrenches] (no subject)
>>>>>>> 
>>>>>>>  
>>>>>>> Interesting so does "require a tool" include taking a screw off the 
>>>>>>> cover plate of the combiner box, too?
>>>>>>> What a game changer.  I'm going to Mexico for my next project; I'll 
>>>>>>> actually enjoy even more being the sole AHJ on the project.  
>>>>>>> 
>>>>>>> R.Ray Walters
>>>>>>> CTO, Solarray, Inc
>>>>>>> Nabcep Certified PV Installer, 
>>>>>>> Licensed Master Electrician
>>>>>>> Solar Design Engineer
>>>>>>> 303 505-8760
>>>>>>> On 4/28/2014 2:52 PM, Michael Morningstar wrote:
>>>>>>> 
>>>>>>> Readily accessible is now defined in the 2014 NEC. Installing OCPD’s 
>>>>>>> underneath a module is a major faux paux, and I can’t imagine any AHJ 
>>>>>>> thinking otherwise. Having to remove a module in order to reset a 
>>>>>>> breaker, what a drag.
>>>>>>> 
>>>>>>>  
>>>>>>> "Capable of being reached quickly for operation, renewal or inspection 
>>>>>>> without requiring those concerned to use a tool, to climb over, remove 
>>>>>>> obstacle or other.”
>>>>>>> 
>>>>>>>  
>>>>>>> Michael
>>>>>>> 
>>>>>>>  
>>>>>>>  
>>>>>>>  
>>>>>>> 
>>>>>>> 
>>>>>>> 
>>>>>>> On Apr 28, 2014, at 10:29 AM, William Miller <will...@millersolar.com>  
>>>>>>>                                 wrote:
>>>>>>> 
>>>>>>> 
>>>>>>> 
>>>>>>> You call it a solar panel, I call it a glass j-box cover plate. 
>>>>>>> 
>>>>>>> William
>>>>>>> 
>>>>>>> Miller Solar
>>>>>>> 
>>>>>>> 
>>>>>>> On Apr 28, 2014, at 9:21 AM, Jason Szumlanski <ja...@fafcosolar.com> 
>>>>>>> wrote:
>>>>>>> 
>>>>>>> If that is the interpretation,
>>>>>>> I don't see how the breakers are "readily accessible" in a SolaDeck
>>>>>>> mounted anywhere, regardless of whether it is under a module. It
>>>>>>> requires removal of four screws (using a tool) to access the breakers
>>>>>>> inside the enclosure. It's all up to the AHJ. It has not been an issue
>>>>>>> locally here. I can see how other jurisdictions may not
>>>>>>> concur.
>>>>>>> 
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to