Allan,

 

The Full River sealed battery line also has charging voltages similar to the
numbers for the Rhino’s. We have had good results with many Full River
battery banks, no premature failures to date. Certainly these are higher
charging voltages than the early VRLA batteries we saw years ago.

 

David Palumbo

Independent Power LLC 

462 Solar Way Drive

Hyde Park, VT 05655

 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan
Sindelar
Sent: Thursday, January 02, 2014 4:01 PM
To: e...@solarnexusinternational.com; RE-wrenches
Subject: Re: [RE-wrenches] Higher LVR to force full re-charge in small OGPV
systems

 

Eric,
Not having previously heard of Rogue Engineering, I looked them up on the
web. 

I would be cautious above using the Rhino-10 product you have identified.
According to the product manual for it at
http://rogue-engr.homestead.com/Manual_1950-162.pdf, it is a 10A PWM
controller labelled and described as being for "SLA" - sealed lead acid
batteries. Yet its specs include a 14.8V bulk voltage - what they call a
"top=off" voltage - and a 14.1V float voltage. 14.8 is well up into the
gassing range for a LA battery. Perhaps they expect that with a 10A maximum
charge capacity, the current will be insufficient to force gassing, but
these values fly against all conventional wisdom. 

Does Rogue Engineering know something that the battery industry doesn't? Or
are they simply, as their name suggests, "going rogue"? And has anyone on
this list used this company's products? 
Allan

Allan Sindelar
 <mailto:al...@positiveenergysolar.com> al...@positiveenergysolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder, Positive Energy, Inc.

A Certified B CorporationTM
3209 Richards Lane
Santa Fe, New Mexico 87507
505 424-1112 office 780-2738 cell
 <http://www.positiveenergysolar.com/> www.positiveenergysolar.com

On 12/31/2013 2:34 PM, Eric Youngren wrote:

Thank you Allan, Dan and Ray for your suggestions.    This is the kind of
feedback I was hoping for! 

I agree that the 75W of PV with 120AH of sealed battery is too low of a
ratio of PV to storage and will not help the batteries last 7 years.
Unfortunately those parts of the design are pre-determined in the bid specs
and I don't think they will allow us to suggest alternatives now.  We need
to win the bid first, then maybe we can suggest some changes..   

MPPT would be great but it's just not in the budget for these little
systems, and like Allan says these systems won't ever experience the cold
daytime conditions where MPPT really shines.   

Looks like Rogue Engineering in Englewood, CO will be able to customize
their Rhino-10 PWM controllers with the LVD and LVR setpoints we choose.
I'm leaning towards Allan's suggested values of 12.0 for LVD and 13.8 for
LVR.   I am fairly certain that many of the systems will be run til the LVD
shuts them off, so 12V will ensure they will not be too deeply discharged,
and forcing them to wait until 13.8V before reconnect will give the
batteries a chance to get back up to a full SOC before the cycle is
repeated.    Yes they will experience shut-downs, but I think that over time
this approach will help them learn to live within the capacity of the
systems and give the batteries the longest life possible.  That, or they
will figure out how to bypass the load controller and run directly off the
batteries!  

I like the Midnite MNBCM battery SOC meter.  It's currently the best 'dummy
light' system monitor out there for small systems like this.   We used them
last year for over 1,000 small systems powering computers in schools in
Tanzania and people seem to understand them easily.     We will include them
in the systems we are offering for this tender.   

Thanks again folks!  Lets hope we win the bid!   

 

Eric

 

On Tue, Dec 31, 2013 at 12:01 PM, Ray Walters < <mailto:r...@solarray.com>
r...@solarray.com> wrote:

I'll chime back in on a few points:

To MPPT or not:  It all gets down to the budget: I find the tipping point to
be around 250 to 400 watts.  My small systems usually don't have MPPT, and
as soon as I get into more than a pair of modules, I'm using the cheaper 60
cell modules with MPPT.
I like Blue Sky's new PWM 30 amp controller that also includes a digital
meter.

Temp compensation:  it all depends on the temperature variation. If its warm
year round, just program the charge settings lower, and as Dan said KISS.

Metering:  Midnite's Battery Capacity Meter was specifically designed for
the African market.  Very simple LED "smiley face, frowny face" reading,
It's cheap, and it actually does a decent job of tracking SOC.  Its not a
Trimetric, but its way better than a volt meter too. 



R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
 <tel:303%20505-8760> 303 505-8760

On 12/31/2013 11:48 AM, Exeltech wrote:

Eric .. Allan .. and all ...

Allan wrote:

Re an MPPT controller: Nope, I wouldn't. First, this is equatorial west
Africa.
It's a tropical climate with hot modules most of the year. MPPT offers the
greatest benefit when the voltage delta-T is greatest: cold modules and
empty
batteries.

*** While Allan is correct about deriving maximum MPPT benefit when the PV
are cold, at 75W per panel, and 120A-H battery, the PV are undersized for
all but very light-duty system usage.  Obtaining the maximum possible charge
current will help lengthen battery life.  If two 12V 40W PV in series could
be economically utilized (vs. one 75W panel) .. it's worth considering.



Second, any controller with MPPT is more complex, and thus more expensive,
than a simple PWM controller.

*** Hence my comment at the top of the suggestion list:  "...  if budget and
circumstances permit...".  If not - go with a basic PWM unit and other
cost-saving measures.  If they're going to hold your feet to the fire on the
"seven year" battery performance requirement, you're going to have to limit
the depth of discharge, and also institute other life-enhancing practices.




Re temperature compensation:....

*** Temperature compensation in this application may be a toss-up between
fully recharging the battery and obtaining maximum battery life.  The choice
here could go either way.  If it's always warm (or hot), compensation may
not be needed.  In fact, it may be beneficial to help maximize the recharge
if the controller thinks the battery is cooler than it really is, which in
turn would push the charge voltage set-point up a bit.  Not knowing the
environment where the systems will be installed makes this decision an
unknown .  Also .. and keeping in mind that there are elevated equatorial
areas where the weather can be cool .. compensation may or may not be a
consideration.



To me the other features of the C12 - four adjustable settings, removable
knobs and 15-minute reserve - were more important than MPPT.

*** There is much to be said for the KISS principle.



Re an LED SOC display: agreed just as Dan stated. Is there one that can be
programmed to lie a little? (The best of these I ever knew was the Photron
Batterylite, gone since around 1998. I wish someone would resurrect that
tiny gem.)

*** With several hundred units in the mix, I'd think a small design house
may be interested.  As long as you're at it, how about adding a low-voltage
disconnect option into the monitor design .. and perhaps even an audible
alarm (with user reset).  Each feature adds $ and complexity.  If the users
will routinely look at such an LED monitor and use power accordingly,
neither of these features would be needed.


Eric .. there's no singular (or simple) answer to your question.  If the
project is going to be awarded on a strictly low-bid basis .. and they're
adamant about seven year battery life .. you're going to have difficulty
meeting their budget AND achieving their system goals.


Happy New Year to all....


Dan




--------------------------------------------
On Tue, 12/31/13, Allan Sindelar < <mailto:al...@positiveenergysolar.com>
al...@positiveenergysolar.com> wrote:

  Subject: Re: [RE-wrenches] Higher LVR to force full re-charge in small
OGPV systems
  To: "Exeltech" < <mailto:exelt...@yahoo.com> exelt...@yahoo.com>,
<mailto:e...@solarnexusinternational.com> e...@solarnexusinternational.com,
"RE-wrenches" < <mailto:re-wrenches@lists.re-wrenches.org>
re-wrenches@lists.re-wrenches.org>
  Date: Tuesday, December 31, 2013, 10:51 AM
  Dan and Eric,

Now I'll respectfully argue with some of Dan's suggestions:

Re an MPPT controller: Nope, I wouldn't. First, this is equatorial west
Africa. It's a tropical climate with hot modules most of the year. MPPT
offers the greatest benefit when the voltage delta-T is greatest: cold
modules and empty batteries. No chance for the former, and we're trying to
get around the latter. If these systems were going to a cold climate I'd
agree with you. Second, any controller with MPPT is more complex, and thus
more expensive, than a simple PWM controller. Given the expressed
competitive-bid budget limitations, MPPT is not a smart place to allocate
costs. Dan is right about the weak C/rate. Spend the money (if you can) on a
second or larger module.

Re cool batteries: agreed, although I don't know how to achieve this.

Re temperature compensation: as much as I push it strongly here, it may not
matter in this case, and may be a hindrance. What's the annual ambient
temperature swing? Again, if it's equatorial lowlands the temperature may
stay around a constant 80º all year. If so, TC is irrelevant. And they
occasionally fail, which can cause settings to mess up. Once again, decide
if the added cost is worth it in this application.

Re an LED SOC display: agreed just as Dan stated. Is there one that can be
programmed to lie a little? (The best of these I ever knew was the Photron
Batterylite, gone since around 1998. I wish someone would resurrect that
tiny gem.)

To me the other features of the C12 - four adjustable settings, removable
knobs and 15-minute reserve - were more important than MPPT.
Allan

Allan Sindelar
 <mailto:al...@positiveenergysolar.com> al...@positiveenergysolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder, Positive Energy, Inc.

A Certified B CorporationTM
3209 Richards Lane
Santa Fe , New Mexico 87507
 <tel:505%20424-1112> 505 424-1112 office 780-2738 cell
 <http://www.positiveenergysolar.com> www.positiveenergysolar.com

  On 12/30/2013 7:32 PM, Exeltech wrote:

Eric,

Allan's recommendations on both points are excellent, and spot-on.


I would add the following suggestions for your controller and system if
budget and circumstances permit:

1) Use a MPPT model controller to enhance the recharge rate under
less-than-ideal conditions.  The PV is already undersized for the battery
you indicated (below).

2) If you get the job .. install the batteries in a location that will keep
them as cool as possible.  Heat is just as detrimental to battery life as is
failure to fully charge.

3) Temperature-compensated charging will enhance battery life.  However, the
75W PV vs. 120 A-H battery allows for only a C/20 recharge rate at best.
This is not conducive to full recharge on a regular basis unless the loads
are very small and are lightly used.  If the budget allows for opportunity
to double the PV wattage .. it would be wise to do so.

4) A simple "stop-light" style LED voltage display won't consume much power,
but can go a long way toward providing a visual indicator for
state-of-charge, especially if it's adjustable, and can be be biased toward
a higher SOC (in essence, make it fib a little, and indicate a low SOC
sooner than than is actually the case).  Worth considering as an option ..
but easily omitted to reduce cost and/or simplify the system.

I wish you success on winning the project.


Regards,


Dan

--------------------------------------------
On Mon, 12/30/13, Allan Sindelar < <mailto:al...@positiveenergysolar.com>
al...@positiveenergysolar.com> wrote:

  Subject: Re: [RE-wrenches] Higher LVR to force full re-charge in small
OGPV systems
  To:  <mailto:e...@solarnexusinternational.com>
e...@solarnexusinternational.com, "RE-wrenches" <
<mailto:re-wrenches@lists.re-wrenches.org>
re-wrenches@lists.re-wrenches.org>
  Date: Monday, December 30, 2013, 6:48 PM
    Eric,
Yes, one of the classic problems with small systems and less educated users.
Just a small contribution: it would seem to me that in this case the LVD
setting is as key as the LVR. What if the LVD was set as high as possible -
say, 12.0 V with sealed batteries, along with a 13.8 - 14.0 V LVR. The
system would still be run until it shuts off, but the battery remains at a
relatively high SOC. The next day the system will return to operation, but
with a much higher range of SOC. The users will still experience shutdown,
and will over time become familiar with when to expect it and how to live
within its capacity, but the battery life will be protected.

This approach seems counter-intuitive, but the more I think about it the
more sense it makes. The system would also return to operation sooner
following cloudy weather - in fact, it would provide a minimal amount during
each of the cloudy evenings.

Is the C12 still made? It would still seem ideal if so: bulk, float, LVD and
LVR, all adjustable, with removable knobs and a 15-minute reserve button
after initial LVD shutdown. Rock-solid reliable, too, in my experience.

I'd be interested in what approach you select. This intrigues me.
Allan

Allan Sindelar
 <mailto:al...@positiveenergysolar.com> al...@positiveenergysolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder, Positive Energy, Inc.

A Certified B CorporationTM
3209 Richards Lane
Santa Fe , New Mexico 87507
 <tel:505%20424-1112> 505 424-1112 office 780-2738 cell
 <http://www.positiveenergysolar.com> www.positiveenergysolar.com

  On 12/30/2013 5:00 PM, Eric Youngren wrote:

Hi Wrenches,

We are bidding on a project to provide several hundred small (75Wpv, 120AH
battery) 12V DC off-grid solar home systems for rural villages in West
Africa.  The project planners have requested that the systems be designed
and built to provide 7 years of battery life.  That seems crazy optimistic
to me but I'm trying to design the systems that will give the batteries a
fighting chance of lasting that long.

In my experience with these types of installations, the system users have
little or no understanding of how to properly manage their batteries and
usually no metering or SOC indication to help them even if they knew what to
look for.  So, the default control strategy becomes:  run the loads until
the Low Voltage Disconnect (LVD) turns them off, then wait until the Sun
returns and the voltage rises to the Low Voltage Reconnect (LVR) setpoint
(around 12.5V is a common default) , upon which point the cycle repeats,
with the result that the battery bounces between LVD and LVR, almost never
reaches a full SOC, and the batteries are lucky to survive for maybe two
years.  After that the system will provide a little power during the day
while the Sun is shining but the batteries will quickly crash below the LVD
after the sun goes down.

So, we want to offer a controller with a high LVR setting that will ensure
the batteries reach a full recharge after each and every LVD incident.    I
know the C-12 has an adjustable LVR setpoint and I see one Chinese brand
(Manson) that can do it.   Does anyone have any other suggestions of small
(<20A) PWM controllers that can be adjusted to not reconnect until 14V or
so?     Price is going to be a factor in this project so they need to be low
cost.

Any other suggestions?  What would you use for the optimal LVD and LVR in
this situation?     These are rural household, DC only systems with
primarily lighting and small device charging loads.   I know that this
strategy will mean that they might not have any access to battery power for
up to a few days if they hit the LVD during the rainy season and there is
not enough sunshine to get the battery charged in a single day.  My thinking
is that experience will provide good feedback that will encourage them to
conserve and manage their batteries to avoid the LVD situation as much as
possible.     That's the idea, anyway.  I'd appreciate any advice from you
all.  Thanks!

Wishing you all a happy and productive 2014!

Best energy,
Eric

_______________________________________________
List sponsored by Home Power magazine

List Address:  <mailto:RE-wrenches@lists.re-wrenches.org>
RE-wrenches@lists.re-wrenches.org

Change email address & settings:
 <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
 <http://www.re-wrenches.org/etiquette.htm>
www.re-wrenches.org/etiquette.htm

Check out participant bios:
 <http://www.members.re-wrenches.org> www.members.re-wrenches.org




_______________________________________________
List sponsored by Home Power magazine

List Address:  <mailto:RE-wrenches@lists.re-wrenches.org>
RE-wrenches@lists.re-wrenches.org

Change email address & settings:
 <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
 <http://www.re-wrenches.org/etiquette.htm>
www.re-wrenches.org/etiquette.htm

Check out participant bios:
 <http://www.members.re-wrenches.org> www.members.re-wrenches.org

 






_______________________________________________
List sponsored by Home Power magazine
 
List Address:  <mailto:RE-wrenches@lists.re-wrenches.org>
RE-wrenches@lists.re-wrenches.org
 
Change email address & settings:
 <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules & etiquette:
 <http://www.re-wrenches.org/etiquette.htm>
www.re-wrenches.org/etiquette.htm
 
Check out participant bios:
 <http://www.members.re-wrenches.org> www.members.re-wrenches.org
 

 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to