Even though they say "Photovoltaic" in the spec sheet, I am not sure that this 
is "PV Wire".  I don't see anywhere that it actually uses those exact words, 
and that is the designation in the NEC.

Blessings,
Kelly



On Sep 27, 2013, at 10:38 AM, August Goers wrote:

> Marco,
>  
> Yes, there is single jacketed PV wire. I've attached a spec sheet for some 
> 1000 V wire we've been using. I don't know anything about the actual wiring 
> construction and why single versus double jacketing may or may not be used. I 
> just know it needs to be listed for the purpose.
>  
> Best, August
>  
> From: re-wrenches-boun...@lists.re-wrenches.org 
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Marco 
> Mangelsdorf
> Sent: Friday, September 27, 2013 10:28 AM
> To: 'RE-wrenches'
> Subject: [RE-wrenches] transformerless inverters and conductor colors
>  
> Thanks, August.
>  
> OK, so I’ve found “PV wire” that’s double-insulated.  (See attached spec 
> sheet from Falcon wire.)
>  
> Is there PV wire out there that’s just got a single insulation layer that 
> qualifies as per what came from that helpful article below?
>  
> marco
> USE-2 is a standard wire designated for underground service entrance, 
> typically used to connect terminals of a variety of service equipment. PV 
> wire is specifically designated for use in PV module interconnections. Both 
> cables are rated for 90oC wet or dry. PV wire, however, has thicker 
> insulation to withstand the harsh environments frequently found in PV 
> installations. USE-2 carries a 600V rating, whereas PV wire can be rated at 
> 600V, 1000V or 2000V. There are separate ratings with increased insulation 
> thickness for each cable.
> 
> Both USE-2 and PV wire can be used with grounded systems, but only PV wire 
> may be used with ungrounded systems per NEC 2008. Since USE-2 has typically 
> been installed underground or in environments where flame is unlikely, it 
> usually does not require a flame retardant rating.The PV wire designation 
> does include a VW-1 flame test requirement. Both ratings are sunlight 
> resistant, but the PV wire rating applies a more stringent test requirement 
> of 720 hours in weatherometer vs. 300 hour weatherometer test for USE-2.
> 
>  
> From: re-wrenches-boun...@lists.re-wrenches.org 
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of August Goers
> Sent: Friday, September 27, 2013 4:18 AM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] transformerless inverters and conductor colors
>  
> Marco,
>  
> My understanding is that PV wire is a separate listing. Exposed DC wiring 
> with ungrounded non-isolated systems must be PV wire. USE-2 wire is not 
> necessarily PV wire unless listed and labeled as PV wire. Here's a decent 
> article:
>  
> http://www.renewableenergyworld.com/rea/news/article/2010/11/performancecost-trade-offs-in-pv-systems-wiringcabling-selection
>  
> Best, August
>  
> From: re-wrenches-boun...@lists.re-wrenches.org 
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Marco 
> Mangelsdorf
> Sent: Friday, September 27, 2013 12:24 AM
> To: 'RE-wrenches'
> Subject: [RE-wrenches] transformerless inverters and conductor colors
>  
> Thanks, Glen.
>  
> This brings up the question of what exactly constitutes “PV Wire.”   “PV 
> wire” does not necessarily = double-insulated wire which I thought is 
> required with ungrounded PV systems on the DC side at least until you hit an 
> enclosure and enclosed raceway where you can transition to THWN-2 wire.  Is 
> there a clear and unambiguous definition out there of what constitutes “PV 
> Wire”?  To some XLP/USE-2/RHW-2 wire is “PV Wire.”
>  
> marco
>  
> 2008 NEC
>  
> 690.35 Ungrounded Photovoltaic Power Systems.
> Photovoltaic power systems shall be permitted to operate with ungrounded 
> photovoltaic source and output circuits where the system complies with 
> 690.35(A) through (G).
> (A) Disconnects.
> (B) Overcurrent Protection.
> (C) Ground-Fault Protection.
> (D)  The photovoltaic source conductors shall consist of the following:  
> (1)          Nonmetallic jacketed multiconductor cables 
> (2)          Conductors installed in raceways, or 
> (3)          Conductors listed and identified as Photovoltaic (PV) Wire 
> installed as exposed, single conductors.
>  
> Raceway.  An enclosed channel of metal or nonmetallic materials designed 
> expressly for holding wires, cables, or busbars, with additional functions as 
> permitted in this Code. Raceways include, but are not limited to, rigid metal 
> conduit, rigid nonmetallic conduit, intermediate metal conduit, liquidtight 
> flexible conduit, flexible metallic tubing, flexible metal conduit, 
> electrical nonmetallic tubing, electrical metallic tubing, underfloor 
> raceways, cellular concrete floor raceways, cellular metal floor raceways, 
> surface raceways, wireways, and busways.
>  
> Reads to me like you can transition to THWN-2 inside a rooftop jbox from the 
> PV wire under the modules, as long as it is in a raceway.
>  
> -Glenn Burt
> <EncoreWire-Photovoltaic 
> (2).pdf>_______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to