Hi Wallace,

For services, at least, in the 2011 NEC, the neutral is still sized per Table 250.66 (250.24 (C) (1).

I took Allan's suggestion and called Power One tech support back. The neutral carries no current; it is strictly for sensing.

Drake

At 02:23 PM 6/20/2013, you wrote:
Drake,

Full sized neutrals are now required due to harmonics at least.

The cost over your quote for neutral is fixed. What is the cost for unknown consequences if you disregard manufacturers specs?

Wallace Stahle
Future Electric Energy Co
P O Box 236
Willits, CA 95490
<mailto:[email protected]>[email protected]
CA Lic.# C10-762093
707-459-0474


On Jun 19, 2013, at 3:26 PM, Drake wrote:

That was my first call. They said use a full size neutral. I'm not satisfied with that answer. The combined experience and knowledge on this list far exceeds that of any tech support person.

At 04:27 PM 6/19/2013, you wrote:
Drake,
Why not discuss this with Power One tech support?
Allan

Allan Sindelar
<mailto:[email protected]>[email protected]
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc., a Certified B CorporationTM
3209 Richards Lane
Santa Fe, New Mexico 87507
505 424-1112 office 780-2738 cell
<http://www.positiveenergysolar.com/>www.positiveenergysolar.com

On 6/19/2013 1:55 PM, Drake wrote:
A very common cable for 100 A service conductors has 2 - #2 AL wires and 1 - #4 AL for the neutral; 200 A will have 2 - 4/0 AL wires and 1 - 2/0 for the neutral. If I run # 2 to limit the VD on the run to the panel and reduce the neutral to #4, #12 copper phase and neutral will still connect to the inverters. This would be code for a feeder to a separate structure.

Does the Power One inverter actually have a major imbalance resulting in substantial neutral currents? If so, it is really a 120 V inverter for VD calculations.


 03:37 PM 6/19/2013, you wrote:
Content-Type: multipart/related;
        boundary="----=_NextPart_000_00A6_01CE6CE9.D20EFB20"
Content-Language: en-us

Doug,
705.95(B) allows you down size your neutral if it is used solely for instrumentation and it must be sized equal to or larger than the EGC but this is not the case. If Power One says a full size neutral is needed than that means that it is not just a voltage sensing conductor used for instrumentation and that it does carry current.

I don't believe there are any exceptions in code for downsizing your neutral in regards to upsizing the conductors to account for voltage drop but I could be wrong.

--
John Stimac | Corvallis, OR
Renewable Energy Associates LLC
541-754-2001 Office/Fax
<mailto:[email protected]>[email protected]
www.renewableassociates.com
<2221ada.jpg>



From: <mailto:[email protected]>[email protected] [ mailto:[email protected]] On Behalf Of Drake
Sent: Wednesday, June 19, 2013 6:42
To: <mailto:[email protected]>[email protected]
Subject: [RE-wrenches] Full sized neutral - 240 V inverter

Hello Wrenches,

Power One tech support said that full sized neutrals had to be run to a pair of 240 V, PVI 3.6 inverters. We have a 180 foot underground run to the service panel.

Why do we need to run a full sized neutral all the way back to the panel? The wiring to the panel is oversized for voltage drop. The code allows for reduction of neutral size where neutral imbalance is less than the current of a phase, which is usually the case.

Why does a neutral need to be installed that is the size of the phase wiring where the imbalance should be negligible? Or is there a lot of neutral current for some reason? Am I missing something?

Thanks

Drake


Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV Installer
740-448-7328
<http://athens-electric.com/>http://athens-electric.com/


_______________________________________________
List sponsored by Home Power magazine

List Address: <mailto:[email protected]>[email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




_______________________________________________
List sponsored by Home Power magazine

List Address:
<mailto:[email protected]>
[email protected]

Change email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:

http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:

www.re-wrenches.org/etiquette.htm

Check out participant bios:

www.members.re-wrenches.org




_______________________________________________
List sponsored by Home Power magazine

List Address: <mailto:[email protected]>[email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: <mailto:[email protected]>[email protected]

Change email address & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to