Hello Wrenches,

Power One tech support said that full sized neutrals had to be run to a pair of 240 V, PVI 3.6 inverters. We have a 180 foot underground run to the service panel.

Why do we need to run a full sized neutral all the way back to the panel? The wiring to the panel is oversized for voltage drop. The code allows for reduction of neutral size where neutral imbalance is less than the current of a phase, which is usually the case.

Why does a neutral need to be installed that is the size of the phase wiring where the imbalance should be negligible? Or is there a lot of neutral current for some reason? Am I missing something?

Thanks

Drake