Just ran in to that. two foot EMT raceway from a production meter into the grid panel. we had to take it out of the emt and run it on the outside to make the inspector happy, I mean, to meet code.
On Thu, Jan 24, 2013 at 10:22 AM, August Goers <aug...@luminalt.com> wrote: > Jesse, > > Any metallic raceway that has a GEC running through it needs bonding. So, > if you've got the Enphase DC-GEC running through it then, yes, it would > need bonding fittings. At least that's my take on it. > > Check out NEC 250.64(E) towards the second half of the paragraph. 2011 NEC > has a nice clarification point and directs you to 250.92(B)(2) through > (B)(4). > > Best, > > August > > > August Goers > > Luminalt Energy Corporation > 1320 Potrero Avenue > San Francisco, CA 94110 > m: 415.559.1525 > o: 415.641.4000 > aug...@luminalt.com > > -----Original Message----- > From: re-wrenches-boun...@lists.re-wrenches.org > [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jesse Dahl > Sent: Thursday, January 24, 2013 8:45 AM > To: Wrenches > Subject: [RE-wrenches] Bonding bushings? > > If you are using micro inverters and terminating them in an AC combiner > panel, does the feed for the AC combiner panel (125A) need to have bonding > bushings for the ground wire? In other words is this ground wire a > GEC/Equipment ground like might be used if running an inverter output to a > panel? The raceway is already in and is EMT. > > Thanks! > > Jesse > > Sent from my iPhone > _______________________________________________ > List sponsored by Home Power magazine > > List Address: RE-wrenches@lists.re-wrenches.org > > Options & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out participant bios: > www.members.re-wrenches.org > _______________________________________________ > List sponsored by Home Power magazine > > List Address: RE-wrenches@lists.re-wrenches.org > > Options & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out participant bios: > www.members.re-wrenches.org > > -- Alex Cozine NABCEP Certified Solar PV Installerâ„¢ Journeyman Electrician Brothers Electric Solar brotherselectricsolar.com
_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org