Jesse, Any metallic raceway that has a GEC running through it needs bonding. So, if you've got the Enphase DC-GEC running through it then, yes, it would need bonding fittings. At least that's my take on it.
Check out NEC 250.64(E) towards the second half of the paragraph. 2011 NEC has a nice clarification point and directs you to 250.92(B)(2) through (B)(4). Best, August August Goers Luminalt Energy Corporation 1320 Potrero Avenue San Francisco, CA 94110 m: 415.559.1525 o: 415.641.4000 aug...@luminalt.com -----Original Message----- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jesse Dahl Sent: Thursday, January 24, 2013 8:45 AM To: Wrenches Subject: [RE-wrenches] Bonding bushings? If you are using micro inverters and terminating them in an AC combiner panel, does the feed for the AC combiner panel (125A) need to have bonding bushings for the ground wire? In other words is this ground wire a GEC/Equipment ground like might be used if running an inverter output to a panel? The raceway is already in and is EMT. Thanks! Jesse Sent from my iPhone _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org