The input breaker to the inverter only needs to be 60 amp to support the load 
and the battery charging capability of the inverter.  You could downsize the 
input breaker if you adjusted thr maximum ac current for battery charging down 
to 5 or 10 amps.
David Katz

Sent from my HTC smartphone on the Now Network from Sprint!


----- Reply message -----
From: "John Berdner" <[email protected]>
To: "[email protected]" <[email protected]>, "RE-wrenches" 
<[email protected]>
Subject: [RE-wrenches] Point of Connection 705.12D2 Exception
Date: Mon, Dec 31, 2012 7:39 am



Greg:

Two part answer...

1) Yes, downsizing the main breaker is one scenario permitted by NEC to 
increase the current of the sources backfiring the panel.  If the bus bars in 
the panel are rated for 200 amps then you are allowed 120% or 240 Amps feeding 
from all sources.  Decreasing the main to 100 Amps (the grid source) would 
allow you to have 140 Amps of "other sources" and not overload the bus bar in 
the panel.

2) As you correctly noted the amount of current from the other sources would 
then exceed the rating of the main breaker.  While the bus bars would be ok you 
would still have a problem because you need to design all the breakers in the 
"upstream" current path to support the 140 Amp load.  If you were to order the 
panel with a 125A main this would be the best configuration.  240 Amps from all 
sources - 125 A main breaker = 115 Amps available for the other sources and, 
since 115 Amps from the other sources would not overload the 125 Amp main, you 
would probably be ok.   The other approach would me to install a secondary 
service (often incorrectly referred to as a line side tap) and interconnect on 
the utility side of the main.  This is what I have at my house with a 100 Amp 
fused disconnect feeding the Sunny Island backup/Gird tied PV system).

Another thing to consider and that is the size of the utility transformer 
feeding the service. While not a Code issue it could be an issue for the 
utility.   In residential services it is relatively common to see a transformer 
that is smaller (sometimes much smaller) than what would be needed to support 
the full load of a 200 Amp main.  At my house I requested a larger transformer 
and they installed a 25 kVA instead of the standard 20 kVA.  In the 115 Amp 
scenario a 20 kVA transformer would be marginal at peak back feed (115A * 240 = 
27.6 kVA / 1.25  = 22.08 kVA continuous).
Lastly, the inspector >>might<< want you to show a calculation to prove the 
125Amp main is large enough to support all the loads onsite.  Pointing out the 
limitations of the transformer feeding the service >> might<< be helpful in 
overcoming this objection (assuming the transformer is big enough to support 
your onsite generation).

Best Regards,

John Berdner
General Manager, North America



3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new address.)
T: 510.498.3201 ext 747
M: 530.277.4894


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg Seelhorst
Sent: Monday, December 31, 2012 6:49 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Point of Connection 705.12D2 Exception

We recently came across this Square D Side-by-side MMC that uses the same 200A 
busbar with a 100, 125, 150 and 200A Main Breakers.  They are interchangeable 
for swapping the Main Breakers.  I had to go to Schneider to get this spec 
sheet which shows the 200A rating for the SC2040M200S series (is followed by a 
100, 125, 150, or 200 after the last 'S').

Question, using William's calculations shown below, if the 100A Main Breaker 
version is used, this would feasibly allow a backfeed 140A of solar, but 
wouldn't this be electrically limited by the Main Breaker's capacity of 100A.  
Of course, not a likely scenario of wanting to backfeed more than the main 
breaker's rating.

Our distributor regularly stocks this because it is so versatile and the Main 
Breakers can be ordered separately when the homeowner wants to upgrade their 
service and only a breaker swap is required.

Greg Seelhorst
Designer/Project Manager
NABCEP Certified Solar PV InstallerT


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of William Miller
Sent: Sunday, December 30, 2012 8:28 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Point of Connection 705.12D2 Exception

Jeremy:

Bingo!  You have discovered the hard truth of grid tie with battery point of 
connection compliance (GTWB POC).  Your inverter will through-transfer up to
60 Amps (A), so to use all of that capability, you should feed it with 60A.
However, you are not allowed to feed the inverter with greater than 40A 
dedicated over-current protection (OCPD).  The arithmetic is:

Buss rating:  200A
Allowed total buss feed:  200A X 120% = 240A Main breaker: 200A Allowed PV
feed:  240A-200A= 40A*


If you can downgrade the main breaker to 150A you can back feed up to 90A.
The arithmetic then is:

Buss rating:  200A
Allowed total buss feed:  200A X 120% = 240A Main breaker: 150A Allowed PV
feed:  240A-150A= 90A

Downgrading the main breaker is not easy.  Most meter/main/combos (MMCs) will 
not allow the downgrade-- there is not a 150A breaker made that is designed and 
listed to fit in the 200 A panel.  I have contacted various manufacturers and 
requested that 200 (MMCs) be made that will readily accept a 150A main breaker, 
but large corporations do not seem to care about the needs of a small part of 
the market..

I had found a 200 A MMC that I could downgrade the main breaker to 150 A, but 
not easily.  The fit was not perfect -- I had to modify the hold down bracket, 
but it passed inspection.  Technically I suppose the MMC was no longer 
compliant with the listing once I modified it, but sometimes you gotta do what 
you gotta do.

Good Luck.

William Miller

* PS:  I believe the 2011 NEC has an exception that applies, but I do not 
believe any jurisdictions are using that code.  I have convinced my local 
building officials to pre-adopt certain future code sections.  Maybe you can 
make the case to your local inspectors.  Meet with them, explain the 
limitations of the XW as far as intertie amperage and maybe they will allow use 
of a 60A breaker.

Wm

At 04:27 PM 12/30/2012, you wrote:
>I'm concerned that the inspector will not allow a 60A back fed breaker
>in the 200A main panel as it exceeds the 120% rule Jeremy Sent via
>BlackBerry. Sorry for typos and shorthand!
>_______________________________________________

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>

CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for 
the use of the individual or entity who is the intended recipient and may 
contain information that is privileged, confidential and exempt from disclosure 
or any type of use under applicable law. If the reader of this e-mail is not 
the intended recipient, or the employee, agent, or representative responsible 
for delivering the e-mail to the intended recipient, you are hereby notified 
that any dissemination, distribution, copying, or other use of this e-mail is 
strictly prohibited. If you have received this e-mail in error, please reply 
immediately to the sender.
P Please think of the environment before printing this email
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to