Per the SI install manual: 

Risk of death from back‑feed into the power distribution grid in the event of 
grid failure.

Once you set the Sunny Boy to stand‑alone grid parameters, the device no longer 
complies

with IEEE 929 and the IEEE 1547.

The out-of-the-box default for the SI is set to not backfeed if the grid goes 
away. The backup function causes the SI to fool the GT inverters into thinking 
the grid’s still around so they keep charging the battery bank even when it’s 
not. And the SI cannot backfeed normally.

If this legal SMA workaround allows backfeeding during blackouts, a function 
that violates UL1741 for you or me to perform, the sentence at the top applies. 

My guess is that the patch allows the SI to run during a blackout and since the 
SI is not designed to be 1709 compliant allowing it to operate with no grid 
signal may pose a threat to the utility. At least that’s what I’m reading. 

 

Jim Duncan

North Texas Renewable Energy Inc

www.ntrei.com <http://www.ntrei.com/>  

NABCEP PV 031310-57

TECL-27398

nt...@1scom.net 

817.917.0527

 

 

 

On 10/18/2012 11:14 AM, Jay Peltz wrote:

Hi Allan

 

I guess I don't understand the utility concern?

Are concerned for their transformers, or

does it have to do with rebates?

 

Thx

 

Jay

 

Peltz power

 

 

 

 

 

 

 


On Oct 18, 2012, at 8:29 AM, Allan Sindelar <al...@positiveenergysolar.com> 
wrote:

Erika,
This just came up for us recently. I learned this, surprisingly, from a 
Customer Generation tech at our local utility. We are installing a GTWB system 
with two SI5048s and two SB5000s. The CG tech spoke with SMA tech support about 
the possibility of the SIs selling back to the utility as well as the SBs. He 
learned that there is a software patch that can be installed in the SIs that 
will allow them to do this, but that SMA will only allow the patch to be 
installed upon receiving written permission from the utility. This was 
sufficient for our utility to consider our system to be a 10kW interconnected 
system.

This is all I know that may help you; I heard nothing about "3 seconds". You 
might want to explore this further with SMA tech support.
Allan

Allan Sindelar
 <mailto:al...@positiveenergysolar.com> al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com <http://www.positiveenergysolar.com/>  

 

 

 

 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to