Erika, I think the takeaway here is that the Island only has that surge power capacity on the protected load side- you wouldn't see this surge on the utility side. SMA should be able to provide this sort of documentation for you.

On 2012/10/18 9:38, Erika Weliczko wrote:
Greetings all.

I recently received this back regarding an interconnection application
proposing a Sunny Island 6048 and a SB7000:

“we have to rate the system at the max output of the inverters, and
since that battery backup has an inverter that can export 11kW, (albeit
for 3 seconds) I have to review the system for a total of 18kW.”

This is a new one on me. I might argue that the SB7000 is upstream of
the SI6048 and really the SI6048 is the point of interconnection, so the
SB7000 is irrelevant. And 3 seconds is not really continuous operation.

It seems that batteryless inverters show continuous output ratings,
though I know there are some that specify a larger than expected OCP for
various reasons, but that is not what the utility cares about.

Any insights here?

Thanks,

Erika

REpower SOLUTIONS

www.repowersolutions.com

P: 216.268.2275

C: 216.402.4458



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to