Mark,
   As far as cutting the jumper for us nightowls, it is easy.  Wait until dark. 
 The sun actually turns off every day!.
And for the new people on the block, polarity can still be determined after 
dark.  All you need is a microvolt to get polarity. 

John
CV Solar

-----Original Message-----
From: benn kilburn <b...@daystarsolar.ca>
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Sent: Tue, Sep 18, 2012 1:48 am
Subject: Re: [RE-wrenches] Short Circuit Cell Damage



Mark,
Shorting the string should not be an issue.  
Unless you work at night, obviously there will be an arc when you cut the 
jumper, so remember to cover the whole string with an opaque covering 
beforehand… I think I remember reading that somewhere?!?!  
Or just be careful, try to do it when the irradiance is low (less current), 
separate the cut wires quickly and make sure you have left enough wire in the 
box so that you are not working with short (and energized) wires in a metal 
box. put a wire nut on one wire while you handle and terminate the other.


A safer method, if possible, would be to leave an easily accessible module 
interconnection un-connected until you have terminated the home run (+)&(-), 
then go back and make the final module interconnection.


Cheers,
benn

DayStar Renewable Energy Inc. 
www.daystarsolar.ca  *  Ph: 780-906-7807 
Construction Electrician Solar Photovoltaic Systems Certified
Certificate # 0007S
HAVE A SUNNY DAY





On 17/09/12 9:50 PM, "Mark Frye" <ma...@berkeleysolar.com> wrote:




Wrenches,


True or False: In a nominal sort of grid tied situation with string Voc 
at about 300 VDC and Isc at about 6 or 7 amps......It is OK to install 
modules on a roof in the sun and short the pos and neg together 
indefinitely.


In other words modules can handle operating at Isc continuously without 
damage. It is only if you get localized shading AND a failed bypass 
diode that damaging hot spot heating can lead to failure?


I am reviewing an installation manual that recommends completing the 
home run by connecting the pos and neg of the string with a single 
jumper cable, folding the cable on itself in order to push it through to 
a j-box and at some point later on, cutting the jumper in the j-box to 
terminate the pos and negs to the home run.


I am concerned both about maintaining the string in a short circuit 
condition and cutting the jumper while energized.


Any thoughts?


Mark Frye
Berkeley Solar Electric Systems






_______________________________________________
ist sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
ttp://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
ww.re-wrenches.org/etiquette.htm
Check out participant bios:
ww.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to