I think the tin plating is to minimize/eliminate galvanic corrosion. Tim plated 
aluminum - now that sounds smart!

Typos courtesy of my iPhone. 

On Aug 27, 2012, at 8:52 PM, benn kilburn <b...@daystarsolar.ca> wrote:

> Kirpal.
> 
> The Ilsco lug GBL-4 also comes with a stainless steel set-screw… as stated 
> here….GBL LAY-IN AL/CU 
> if that is all it takes to use the AL lug outdoors (stainless steel 
> set-screw), then why have we been steered towards the 'direct burial rated' 
> tin-plated copper lug instead of an AL lug with SS set-screw?  
> 
> I'm not trying to make a case to not use the SGB lug, I like it and would 
> like to keep some in stock, as they seem pretty useful, I just want to have 
> my bases covered if/when an inspector questions me on them being approved for 
> the application.
> 
> Dan,
> Agreed!  Been trying to get an answer from Ilsco, just tracking down the 
> right person with the answers.
> 
> Cheers,
> benn
> 
> DayStar Renewable Energy Inc. 
> www.daystarsolar.ca  *  Ph: 780-906-7807 
> Construction Electrician Solar Photovoltaic Systems Certified
> Certificate # 0007S
> HAVE A SUNNY DAY
> 
> On 27/08/12 5:42 PM, "Kirpal Khalsa" <solarwo...@gmail.com> wrote:
> 
> Benn...it looks like that lug has "stainless hardware for corrosion 
> resistance"  as stated on the brochure....That would be the biggest 
> consideration as David Brearly mentioned earlier in regards to rust 
> potential.  Stainless hardware and tin plating is equivalent to the WEEB 
> lugs....Tin plating and stainless hardware is as good as anything else 
> available as far as outdoor ratings are concerned.....
> I see your point that it is not explicitly stated for outdoor use....however 
> being marketed for use with solar panels also seems to imply rather obviously 
> that it is outdoor rated.....in my unofficial opinion.  
> 
> -- 
> Sunny Regards,
> Kirpal Khalsa
> NABCEP Certified Solar PV Installer
> 
> 
> 
> On Mon, Aug 27, 2012 at 4:11 PM, benn kilburn <b...@daystarsolar.ca> wrote:
> Thanks for the feedback Wrenches, lots of interesting comments,
> 
> However I'm still wondering…..
> How does one confirm that it is specifically approved for outdoor use?  
> Other than assuming it is implied (because it is 'marketed' as a solar lug).  
> As far as I can tell UL 467 does not imply "outdoor rated" as the aluminum 
> lug "GBL-4" is also UL467 listed.  See here…GBL LAY-IN AL/CU.  
> 
> As well, and as Gary pointed out with his second link, for a module 
> bonding/grounding method to be acceptable, it must be recognized by the 
> module manufacturer, no?
> Which means that any new bonding product on the market must have the blessing 
>  of each mod mfgr.  
> (by way of letter or mention in its install manual).  I have come across 
> inspectors that actually look for this.
> 
> Jason, 
> you wrote "I like the looks of that lug. However, I've been using WEEBs too 
> long to go back now." I agree, and i'm not looking to replace weebs with 
> these, but these certainly seem to have a place in the What do you use for 
> the bonding connection from the ?rails?  
> This SGB lug was suggested for this purpose as well.
> 
> 
> Benn
> DayStar Renewable Energy Inc. 
> www.daystarsolar.ca  *  Ph: 780-906-7807 
> Construction Electrician Solar Photovoltaic Systems Certified
> Certificate # 0007S
> HAVE A SUNNY DAY
> 
> On 27/08/12 2:35 PM, "Gary Willett" <g...@icarussolarservices.com> wrote:
> 
> Here's the Ilsco listing from UL, where it's classed as "Grounding and 
> Bonding Equipment":
> http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/showpage.html?name=KDER.E34440&ccnshorttitle=Grounding+and+Bonding+Equipment&objid=1074099002&cfgid=1073741824&version=versionless&parent_id=1073988940&sequence=1
> 
> The GuideInfo for Grounding & Bonding Equipment lists:
> Grounding and Bonding for Photovoltaic (PV) Systems — Grounding and bonding 
> equipment intended for use in PV systems are additionally investigated in 
> combination with the PV module/panel (see QIGU) to the applicable 
> requirements for such products. Installation instructions provided with the 
> PV system (see QIGU) identify the specific grounding and bonding device that 
> has been investigated and intended for use with that system.
> http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/showpage.html?&name=KDER.GuideInfo&ccnshorttitle=Grounding+and+Bonding+Equipment&objid=1074098839&cfgid=1073741824&version=versionless&parent_id=1073988940&sequence=1
> 
> 
> Regards,
> 
> Gary Willett, PE
> On 8/27/2012 3:20 PM, David Brearley wrote:
>> Yes, sorry. I wasn't speaking of this lug...I like the redesign. Looks 
>> quicker and easier and robust.
>> 
>> On Aug 27, 2012, at 3:17 PM, Jason Szumlanski wrote:
>> 
>>> Yeah, but this one is marketed as a solar bonding lug. I think it's safe to 
>>> say that it appropriately rated for outdoor use. It's always good to 
>>> double-check, of course.
>>> 
>>> Jason Szumlanski
>>> Fafco Solar
>>> 
>>> 
>>> 
>>> On Mon, Aug 27, 2012 at 4:11 PM, David Brearley 
>>> <david.brear...@solarprofessional.com> wrote:
>>> Some of the aluminum lugs are indoor-rated. They have a set screw will rust 
>>> in an outdoor environment. That's one of the classic John Wiles slides. I'd 
>>> just watch out for that....
>>>> 
>>>> On Aug 27, 2012, at 12:53 PM, Brian Mehalic <br...@solarenergy.org> wrote:
>>>> 
>>>>> I believe the UL467 listing means that it is rated for direct 
>>>>> burial/outdoor use.
>>>>> 
>>>>> Brian Mehalic 
>>>>> NABCEP Certified Solar PV Installer™ R031508-59
>>>>> IREC ISPQ Certified Affiliated Instructor/PV US-0132
>>>>> 
>>>>> PV Curriculum Developer and Instructor
>>>>> Solar Energy International
>>>>> http://www.solarenergy.org
>>>>> .org
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
> 
> 
> 
> 
> _______________________________________________ List sponsored by Home Power 
> magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: 
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules 
> & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: 
> www.members.re-wrenches.org
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org