HI Brian,

I would go out and measure the load and  see what it really is as age and 
unknowns might have caused this to change.

But without knowing what the duration/cycle time and kW of the pump is its 
pretty hard to size the battery bank.

Jay

peltz power
On Feb 15, 2012, at 11:04 AM, Brian Teitelbaum wrote:

> Alan and Larry,
>  
> My Franklin Motor book says that a 230VAC single-phase 3HP pump motor has a 
> locked rotor amp rating of 83.4A, and a “max load’ of 3400W. Franklin 
> recommends a 40A breaker for this motor.
>  
> A single OutBack Radian should start it, but it’s close. The Radian spec 
> sheet says 100A at 240VAC for 1 ms, and 70.7A for 100 ms. It also states a 
> 16.97 kVA 100 ms surge
>  
> Very iffy, although I think that it will work. You might want to contact 
> OutBack about it rather than taking the chance. Or plan on two Radians.
>  
> Brian Teitelbaum
> AEE Solar
>  
> From: re-wrenches-boun...@lists.re-wrenches.org 
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Larry 
> Crutcher, Starlight Solar Power Systems
> Sent: Wednesday, February 15, 2012 10:38 AM
> To: al...@positiveenergysolar.com; RE-wrenches
> Subject: Re: [RE-wrenches] Design Question re Battery Bank Sizing
>  
> Alan,
>  
> See if you can find the locked rotor amps (LRA) for this pump. Design to 
> provide that much current for starting the pump. My guess is about 7-9kW for 
> a 3HP.
>  
> I'm not a fan of multiple parallel strings but you are correct that parallel 
> strings will produce more instantaneous current. However in this case, I 
> don't recommend it. Even with other loads it is not likely you will demand 
> more than 250 amps @ 48Vdc draw on the battery to start the pump. That is not 
> excessive for an AGM battery, especially since it is very short duration. 
>  
> If you need more battery capacity, opt for lower voltage batteries instead of 
> paralleling.
> 
> Larry Crutcher
> Starlight Solar Power Systems
> (928) 342-9103
>  
>  
>  
>  
> On Feb 15, 2012, at 10:53 AM, Allan Sindelar wrote:
>  
> Esteemed fellow Wrenches,
> We need to size a battery bank for a GTWB just for starting a well pump. The 
> well is on its own meter, so as long as the battery voltage does not crash 
> when the pump starts there will be plenty of capacity left over for minimal 
> loads.  We'll be using sealed batteries, most likely Concorde SunXtenders. 
> According to theSunXtender Technical Manual, Concordes can handle up to a 
> C/0.2 charge rate (500A for a 100Ah battery), but there is no discussion of 
> maximum discharge rates or voltage drop due to large surge loads.
> 
> The pump is 3HP and is conventional 3-wire, not soft-start. The well is 
> 940ft. and the depth to water is unknown. It pumps into a pressure tank, not 
> open discharge. Customers are not interested in replacing the pump, but might 
> be talked into adding a soft start Franklin controller, although at this 
> preliminary design stage we're not certain one is available for this 
> particular model. The inverter would be a Radian, so system voltage is 48V.
> 
> I would think that configuration would make a difference, as well as size. 
> Using 12V batteries in series/parallel would minimize interconnect and 
> terminal resistance. I think that it would also allow multiple paths for 
> discharge current, reducing the voltage dip.
> 
> What's your best guess at the smallest size battery bank that would reliably 
> start this pump, and how would it best be configured? 
> 
> Thank you,
> Allan
> 
> 
> Allan Sindelar
> al...@positiveenergysolar.com
> NABCEP Certified Photovoltaic Installer
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Positive Energy, Inc.
> 3201 Calle Marie
> Santa Fe, New Mexico 87507
> 505 424-1112
> www.positiveenergysolar.com
> 
> 
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
>  
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to