Separately-derived means that there is physical isolation between two circuits 
in the same electrical system – usually this involves two circuits connected by 
a transformer

The DC side is separately derived in a transformer-based PV inverter. Most 
grid-tie inverters have a DC main bonding jumper internally. Other inverters 
(esp. small stand-alone inverters) may not, and so a main bonding jumper will 
need to be installed.

Jeffrey Quackenbush
NABCEP-certified PV Installer


________________________________
 From: Dave Palumbo <d...@independentpowerllc.com>
To: 'RE-wrenches' <re-wrenches@lists.re-wrenches.org> 
Sent: Tuesday, January 24, 2012 6:43 AM
Subject: Re: [RE-wrenches] Grounding Separately Derived AC System
 

Regarding NEC Article 250.30 does Informational Note #1 mean that a standard 
(no battery) grid-tied PV system is not a Separately Derived System?
 
I’m primarily interested on the consensus view of Bonding the Neutral (grounded 
conductor) to Equipment Ground in a 60 Amp Fused Disconnect located between the 
240VAC inverter output and AC point of connection on the load side of the meter 
in the service disconnect enclosure in a supply side connected PV system. 
 
250.30 Informational Note 1 reads: “An alternate ac power source, such as an 
on-site generator, is not a separately derived system if the grounded conductor 
is solidly interconnected to a service-supplied system grounded conductor…”   I 
believe a  PV system meets that description as the Neutral stays connected at 
all times. 
 
My interpretation is that a standard net-metered PV system is therefore not a 
separately derived system and the Neutral should not have a bonding jumper to 
equipment ground in the Fused Disconnect.
 
Is this the correct interpretation?
 
David Palumbo
Independent Power LLC 
462 Solar Way Drive
Hyde Park, VT 05655
www.independentpowerllc.com 
NABCEP Certified PV Installer
Vermont Solar Partner
24 Years Experience, (802) 888-7194 
 
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to