I agree and read it the same way. Not a separately derived system. 

Jesse 

Sent from my iPhone

On Jan 23, 2012, at 7:13 PM, "Dave Palumbo" <d...@independentpowerllc.com> 
wrote:

> Regarding NEC Article 250.30 does Informational Note #1 mean that a standard 
> (no battery) grid-tied PV system is not a Separately Derived System?
>  
> I’m primarily interested on the consensus view of Bonding the Neutral 
> (grounded conductor) to Equipment Ground in a 60 Amp Fused Disconnect located 
> between the 240VAC inverter output and AC point of connection on the load 
> side of the meter in the service disconnect enclosure in a supply side 
> connected PV system.
>  
> 250.30 Informational Note 1 reads: “An alternate ac power source, such as an 
> on-site generator, is not a separately derived system if the grounded 
> conductor is solidly interconnected to a service-supplied system grounded 
> conductor…”   I believe a  PV system meets that description as the Neutral 
> stays connected at all times.
>  
> My interpretation is that a standard net-metered PV system is therefore not a 
> separately derived system and the Neutral should not have a bonding jumper to 
> equipment ground in the Fused Disconnect.
>  
> Is this the correct interpretation?
>  
> David Palumbo
> Independent Power LLC
> 462 Solar Way Drive
> Hyde Park, VT 05655
> www.independentpowerllc.com
> NABCEP Certified PV Installer
> Vermont Solar Partner
> 24 Years Experience, (802) 888-7194
>  
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to