Jay:
I disconnected the AGS and the problem persisted. Adding a load may help
but I did not test this. This would require a permanent load and might not
be desirable.
William
At 07:36 AM 9/9/2011, you wrote:
Hi William,
is the problem the actual connection or the AGS?
if its the actual connection, have you tried putting a load ( say 1000
watt heater) on the generator directly to stabilize the volt/hz from the
genny?
if for a test if nothing else.
jay
peltz power
On Sep 8, 2011, at 9:40 PM, William Miller wrote:
Friends:
Working yesterday on a newer XW system with a new Kohler RES15
generator. This is the first time I have tested the inverter with this
generator. The inverter would not maintain a transfer to the
generator. After about an hour on the phone with tech support, the tech
searched previous calls and announced that there is a known
incompatibility between the Kohler RES15 and a certain version of the XW
firmware. I was advised to upgrade the firmware.
I wonder how this can be. Voltage and frequency even in the moment the
inverter did try to connect are well within specifications. After some
thought, all I can guess is that there might be some noise on the AC
signal that the inverter might reject.
Has anyone else experienced this? Any insight to be offered?
Thanks in advance.
William Miller
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org