I thought (based a previous thread) that we needed to be concerned with VA 
output of inverters, not wattage, at least on the transformer based machines 
like the SW.
I realize this wouldn't be an actual load if on grid.
In these situations, I just measure DC amps into the inverter to determine the 
actual consumption,  irregardless of power factor, AC efficiency, etc.

R. Walters
r...@solarray.com
Solar Engineer




On Jul 25, 2011, at 9:29 AM, Exeltech wrote:

> Measuring current without the phase relationship between the current and 
> voltage
> isn't indicative of the actual power consumed.  Likely what you were seeing 
> is the
> eddy current in the transformer core.  If so, it's 90 degrees out of phase 
> with the
> voltage, and the real wattage consumed with no load connected is minimal.
> 
> Dan
> Sr. Engineer
> Exeltech
> 
> 