On 7/19/2011 2:34 PM, David Brearley wrote:
Presumably the latter---added as part of the cycle of revisions initiated in 1987.


The array shorting requirement must have gone away near 1993 or 1994 as
I designed an opening and  shorting of the array style GFPD version in
1994 while at Trace Engineering.

It  would have been expensive.

boB









On 7/19/11 3:29 PM, "Hans Frederickson" <h...@fredelectric.com> wrote:

    David,
    Thanks for the interesting history on GFPDs. My copy of the 1987
    NEC does not have 690-5, and it's not missing any pages. Either my
    code book is an incomplete printing or perhaps John Wiles was
    referring to a 1987 proposal that didn't make it into the code
    until the 1990 NEC.

    Regards,
    -Hans

    ------------------------------------------------------------------------
    *From:* re-wrenches-boun...@lists.re-wrenches.org
    [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of
    *David Brearley
    *Sent:* Tuesday, July 19, 2011 12:57 PM
    *To:* RE-wrenches
    *Subject:* Re: [RE-wrenches] 1987 NEC

    Hans,

    John Wiles described the evolution of this standard for a Home
    Power article that we referenced later in a SolarPro on PV System
    Ground Faults:

    http://solarprofessional.com/article/?file=SP2_5_pg60_Mync

    "As described by John Wiles, program manager for the Institute for
    the Energy and the Environment, in the February/ March 2008 Home
    Power article "Ground-Fault Protection Is Expanding," Article
    690.5 was added to the /NEC/ in 1987. One of Wiles' first projects
    in the PV industry was to develop "prototype hardware" to meet the
    new /Code/ requirement. "The basic concept (of the original GFPD
    prototype)," writes Wiles, "was to insert a 0.5- or 1-amp circuit
    breaker in the dc system-bonding conductor." This small circuit
    breaker senses any current between the grounded current-carrying
    conductor and the grounding system, tripping if current exceeds
    the 0.5 A or 1 A rating. By mechanically linking this smaller
    breaker to larger capacity breakers that are installed inline with
    the ungrounded current-carrying array conductors, it is possible
    to detect, interrupt and indicate that a ground fault has
    occurred, and to disconnect the fault.

    These early GFPDs were manufactured for 48 V or lower PV systems.
    According to Wiles, "As higher voltage, utility-interactive PV
    inverters became available in the late 1990s, using a 0.5- or
    1-amp fuse as the sensing element and the inverter's control
    electronics to monitor the fuse was more cost effective." While
    the sensing equipment may have changed, in general the role of the
    modern GFPD remains the same as it was in 1987:

    1. Detect ground faults in PV arrays.
    2. Interrupt the fault current.
    3. Indicate that a ground fault has occurred.
    4. Disconnect the faulted part of the array.

    These four GFPD requirements for grounded PV arrays are spelled
    out in /NEC/ 690.5(A) and 690.5(B). The former requires
    ground-fault detection and interruption (GFDI), which includes the
    provision to indicate the presence of a ground fault. The latter
    requires that faulted circuits be isolated either by disconnecting
    the ungrounded conductors of the faulted circuit or by shutting
    down power to the output power circuits of the inverter or charge
    controller.

    A final GFPD requirement is found in Article 960.5(C), which calls
    for a visible warning in the proximity of the ground-fault
    indicator. The warning could be an LED, an LCD or both. In
    general, the manufacturer provides this electric shock hazard
    warning as part of the listed grid-tied inverter or charge
    controller. However, where a PV system includes batteries, the
    installer must apply a duplicate warning label near the batteries,
    stating:

    WARNING
    ELECTRIC SHOCK HAZARD
    IF A GROUND FAULT IS INDICATED, NORMALLY
    GROUNDED CONDUCTORS MAY BE UNGROUNDED
    AND ENERGIZED


    One change in the GFPD requirements introduced in 1987 is that it
    is no longer necessary to short-circuit, or "crowbar," the PV
    array in the event of a ground fault. This added step had the
    effect of reducing the PV array voltage to zero, minimizing shock
    hazard. The requirement was dropped in a subsequent /Code/ cycle,
    as leaving the array in a short-circuited condition created
    several other issues."


    If you're a Home Power subscriber, you can access the original
    article in the HP archives. If not, it is summarized above.

    Best,

    David Brearley, Senior Technical Editor
    /SolarPro/ magazine
    NABCEP Certified PV Installer ^(TM)
    david.brear...@solarprofessional.com
    Direct: 541.261.6545


    On 7/19/11 2:19 PM, "Hans Frederickson" <h...@fredelectric.com> wrote:

        Kent,
        I'm not a geezer yet, but thanks to my dad I do have a  copy
        of the 1987 NEC. 690-5 (Ground Fault Detection and
        Interruption) was  added in the 1990 NEC. There is no 690-5 or
        mention of ground fault  detection/interruption in the 1987 NEC.

        In the 1990 NEC, section 690-5 is very small compared to 690.5
        in  the 2011 NEC. Here's the complete text from 1990:

        "690-5. Ground Fault Detection and Interruption.  Roof-mounted
         photovoltaic arrays located on dwellings shall be provided
        with ground-fault  protection to reduce fire hazard. The
        ground-fault protection circuit shall be  capable of detecting
        a ground fault, interrupting the fault path, and  disabling
        the array."

        The handbook for 1990 goes on to say that the gfp device  must:
        1) detect the ground fault
        2) open the grounded conductor to  interrupt the ground fault
        3) open the ungrounded conductors and short the  photoltaic
        array source to disable it

        For some reason, I've never heard of item #3, specifically the
        part  about shorting the array. Can anyone shed light on  this?

        Regards,
        -Hans


        ------------------------------------------------------------------------
        *From:* re-wrenches-boun...@lists.re-wrenches.org
         [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf
        Of *Kent Osterberg
        *Sent:* Monday, July 18, 2011 10:07  PM
        *To:* g...@icarussolarservices.com;  RE-wrenches
        *Subject:* Re: [RE-wrenches] 1987 NEC

        Gary,

        No one else has  come up with a 1987 NEC. If you can get a
        copy of 1987 section 690.5 (I think  it was 690-5 back then),
        I'd appreciate it.

        Kent Osterberg
        Blue  Mountain Solar



        Gary Willett wrote:

            Kent:

            I am a member of the  International  Association of
            Electrical Inspectors (IAEI), and they're  headquartered
            here in  the Dallas area.

            If you aren't successful  getting the info from a  Wrench
            with the 1987 code book, let me know  and I am sure I can
            request a  FAXed copy of 1987 section  690.5.





            Regards,

            Gary Willett, PE
            g...@icarussolarservices.com

            On  7/15/2011 4:30 PM, Kent Osterberg  wrote:

                I'm looking  for the text of 1987 NEC 690.5  to
                compare with 2011 version. If any of you  geezers have
                kept copies  that old, please contact me off list.
                Thanks.

                Kent Osterberg
                Blue Mountain Solar
                _______________________________________________




    ------------------------------------------------------------------------





_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options&  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules&  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to