I need to give a group of California educators the simplified explanation of inverter anti-islanding. I know the full details are quite complicated and have evolved a bit over the past few years, but would the following be an acceptable short explanation?
*** Please contact me off-list with comments & edits. Thanks. *** This is an excerpt from a longer discussion about designing and installing grid-tied "Inverter anti-islanding is a requirement of the NEC and the Underwriters Laboratory test procedures. A somewhat over-simplified version of anti-islanding says that if the grid voltage goes out of the range of 216 to 264 Vac or if the grid frequency goes out of the range 59.9 to 60.1 Hz, the inverter must shut down within one cycle (1/60th of a second). Once in this shutdown mode, the grid must come back into compliance (both frequency and voltage) for 5 continuous minutes before the inverter may turn on again. This is pretty ho-hum. However, two of our laboratory sessions involve building a real, grid-connected PV system. So when our students go to turn on their system for the first time, they get to experience the anti-islanding function first hand." Peter T. Parrish, Ph.D., President California Solar Engineering, Inc. 820 Cynthia Ave., Los Angeles, CA 90065 CA Lic. 854779, NABCEP Cert. 031806-26 peter.parr...@calsolareng.com Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885 _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org