On 6/2/2011 6:44 PM, d...@foxfire-energy.com wrote:
What I like best about Mark's set up (the retired phone co. dude w/ half a hand), is that he can select individual strings at random. he can eq an individual string, or top off a few strings and park them. he can even run strings of T 105s, or even nicad (individually of course) in the same system as L-16s and the like.. he just reprograms the chargers (and logs it). I think he got the design from his days in the Navy.

So boB, how about a controller that can be user programed to charge multiple battery configurations with a soft switch? i.e. Bank A, Bank B...? and while you're at it, maybe a multiple string DC box? Something with a shunt and a breaker for each string? A four string set up would be nice.

I could use 2% of your first million.

db


Well, It's not a bad idea !   I'll forward that question off to Robin.
I have ran into several that use separate and independent battery banks
and switch between them. I'm not sure why they don't just use those L-16 size
2V cells though instead.

But as I mentioned before, I think that a battery balancer device would take
care of  problems with single strings but maybe even parallel strings,
as well as the pesky problem of AGM batteries that like to plump when
you cook 'em !  (I hate when that happens and one battery gets real hot)

Say, maybe a gizmo that goes across each battery (no 2V cells though) to keep each battery in the string at the same voltage. It would have to be cheap, maybe $30.

Great discussion.

boB




Dan Brown
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
www.Foxfire-Energy.com <http://www.Foxfire-Energy.com>
NABCEP #092907-44




    -------- Original Message --------
    Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison
    From: boB Gudgel <b...@midnitesolar.com <mailto:b...@midnitesolar.com>>
    Date: Thu, June 02, 2011 8:56 pm
    To: RE-wrenches <re-wrenches@lists.re-wrenches.org
    <mailto:re-wrenches@lists.re-wrenches.org>>



    Nobody mentioned this in this thread, but it occurs to me that the
    answer may be made clearer
    by looking at the Voc of each battery string after so many
    Amp-Hours (years) of service.

    i.e., disconnect the strings' parallel connection and measure the
    individual string voltage after charging them all the best that
    can be done.

    This would be  making the assumption that the batteries themselves
    were fairly equal capacity and voltage at installation time.

    And for whatever reasons, connections, temperatures and everything
    else discussed here, the strings degrade differently.

    The older and more worn out batteries should have a lower voltage
    (Voc) than the less worn out strings. Thus, the better strings
    may be tending to hold up the worse strings by dumping charge into
    them when the whole bank is discharging,
    and wasting energy and battery efficiency.

    I guess that just large 2V cells are the answer in this case, if
    at all possible.

    Thanks for the help on this question !

    boB



    On 6/2/2011 10:42 AM, Tom Elliot wrote:
    Not surprised at all about the phone company guy.  It was a phone
    company guy who read me the riot act that no one in their right
    minds would ever parallel battery banks the way PV off-grid
    systems did and got me to set up my system with separate strings
    connected independently to buss bars.  The battery engineer I
    talked to years ago at Dynasty not only said the same thing but
    also said keeping strings separate meant individual string
    distance from the bars became irrelevant (given correctly sized
    wire for each string’s parallel connectors).  I had a system with
    12 100 amphour strings of paired 12v Dynasty AGMs which was rock
    solid until the day I sold the house.   The last time I checked
    the system before the sale no single battery varied from any
    other in the system by more than 1/10 volt and the majority were
    still holding identical voltages.
    *From:* d...@foxfire-energy.com <mailto:d...@foxfire-energy.com>
    *Sent:* Wednesday, June 01, 2011 4:14 PM
    *To:* RE-wrenches <mailto:re-wrenches@lists.re-wrenches.org>
    *Subject:* Re: [RE-wrenches] 24 volt Battery Bank comparison
    Good thread. Thanks.
    In my experience, it all boils down to the customer. I've seen
    one temp. set up with like 12 strings (for a concert). but they
    were recharged and sold individually within a few weeks.. I've
    also seen a single string (Teledyne aircraft batteries) fail in
    less than a year.. they were in a brand new airplane tug that was
    never charged -- ever. (the guy said "I dunno, it just stopped
    working").
    I have one customer who (last I knew) was running 6 strings of
    mixed aged L-16s going on 8 years. Thing is, he's a retired phone
    company dude (Who's missing half of his right hand from using one
    of those pocket pal screwdriver thingys on a key chain in a hot
    DC rack.. like he'd done hundreds of times before.. but that's
    another tale). But I do like his set up.. he has each string set
    up with it's own fused Disco and Trimetric.. Gives him random
    control over each string. And yes, he keeps a very detailed log,
    and you can bet that when he takes a battery out of service, it's
    done.
    Me? for an average bullet proof off grid system, I shoot for a
    max of two strings for 24V systems (for the redundancy), and
    manually reconfigure them every few years. for 48V systems, I
    shoot for one string of two Volt cells.. thinking that if I loose
    a cell I can still operate a 46V system until I get a replacement.
    And Yes, as we all know, there are folks out there that really
    shouldn't be allowed to operate a popsicle stick.
    db

    Dan Brown
    Foxfire Energy Corp.
    Renewable Energy Systems
    (802)-483-2564
    www.Foxfire-Energy.com <http://www.Foxfire-Energy.com>
    NABCEP #092907-44


        -------- Original Message --------
        Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison
        From: Michael Welch <michael.we...@re-wrenches.org
        <mailto:michael.we...@re-wrenches.org>>
        Date: Wed, June 01, 2011 1:43 pm
        To: RE-wrenches <re-wrenches@lists.re-wrenches.org
        <mailto:re-wrenches@lists.re-wrenches.org>>

        Every now and then I see reference on this list to the need
        for thermal detection. Here is an interesting, inexpensive
        piece of equipment that could be used for finding hot (loose
        or corroded) connections, hot batteries, hot PV cells in
        modules, and even poorly insulated spots, its original
        intended purpose:

        http://www.blackanddecker.com/power-tools/TLD100.aspx

        I have one and used it for finding uninsulated spaces, but
        cannot attest to its durability or suitability for the other
        uses mentioned above.


        boB Gudgel wrote at 01:00 AM 6/1/2011:

        >This might be a good reason for an installer to have one of
        those FLIR (or similar) thermal imager cameras.  They're a
        bit on the expensive side, but could
        >really be helpful for so many things.  Even just to know if
        you have left a nut loose (under load of course)
        >
        >boB


        _______________________________________________
        List sponsored by Home Power magazine

        List Address: RE-wrenches@lists.re-wrenches.org
        <mailto:RE-wrenches@lists.re-wrenches.org>

        Options & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive:
        http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out participant bios:
        www.members.re-wrenches.org <http://www.members.re-wrenches.org>

    ------------------------------------------------------------------------
    _______________________________________________
    List sponsored by Home Power magazine

    List Address: RE-wrenches@lists.re-wrenches.org

    Options & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm

    Check out participant bios:
    www.members.re-wrenches.org

    ------------------------------------------------------------------------
    No virus found in this message.
    Checked by AVG - www.avg.com <http://www.avg.com>
    Version: 10.0.1375 / Virus Database: 1511/3673 - Release Date:
    06/01/11


    _______________________________________________
    List sponsored by Home Power magazine

    List Address:RE-wrenches@lists.re-wrenches.org

    Options&  settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    
List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules&  etiquette:
    www.re-wrenches.org/etiquette.htm

    Check out participant bios:
    www.members.re-wrenches.org


    ------------------------------------------------------------------------
    _______________________________________________
    List sponsored by Home Power magazine

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Options & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options&  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules&  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to