Jason:

A possible solution might be a 3-pole / 3-wire manual transfer switch, or an automatic transfer switch that has manual transfer capability.

If the three Xantrex XW inverters are in a WYE configuration and set up as a "separately derived system", you will need a 4-pole / 4-wire ATS so the neutral can be switched too.

   Put the 3-phase grid connection on the "utility in" of the ATS

   Put the 3-phase service panel on the "load out" of the ATS

   Put the Xantrex 3-phase AC outputs on the "generator in" side of the ATS


Here are some sources you may want to peruse:

   EMERSON / ASCO:
   
http://www.emersonnetworkpower.com/en-US/Products/PowerSwitchingandControls/PowerTransferSwitches/Pages/default.aspx

   GENERAL ELECTRIC:
   http://www.gedigitalenergy.com/powerquality/ATSHome.htm

   RONK: http://www.ronkelectrical.com/pdfstech/METERRITE%20GL.pdf

   EATON / CUTLER-HAMMER:
   
http://www.eaton.com/Electrical/USA/ProductsandServices/ElectricalDistribution/ATS/index.htm


Regards,

Gary Willett, PE

Icarus Engineering / Solar Services LLC
NABCEP Certified Solar PV Installer # 031310-246



<mailto:g...@icarussolarservices.com>

On 5/16/2011 3:34 PM, Jason Szumlanski wrote:
I am looking for an external output bypass assembly for a Xantrex 3 x
XW4024 system. My customer wants to be able to completely bypass the
inverter output and operate loads straight from the grid - similar to
what can be done in an Outback FlexWare system with their I/O bypass
assemblies.

This customer just wants the option of running loads direct from
utility. It has nothing to do with the inverter input side.

Any off-the-shelf solutions out there?

Jason Szumlanski
Fafco Solar




_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options&  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules&  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to