NEC 310.4 permits parallel conductors of 1/0 or larger.  Conductors smaller 
than 1/0 are permitted, but with stipulations.

Nick's assertion "most if not all of the current will flow on the larger wires" 
is incorrect. The current will be shared proportionately between two paralleled 
conductors commensurate with their individual resistances.

The original query related to recreational vehicle PV DC-side installation, and 
referenced installation of a "second PV", implying only one existed initially.  
This would thus fall outside the bounds of the NEC, but shouldn't be 
interpreted to mean some of the common-sense aspects of the NEC aren't to be 
considered.

Dan



--- On Wed, 2/2/11, Jason Szumlanski <ja...@fafcosolar.com> wrote:

From: Jason Szumlanski <ja...@fafcosolar.com>
Subject: Re: [RE-wrenches] Parallel wire runs to increase size
To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
Date: Wednesday, February 2, 2011, 11:15 AM

Nick,  Can you cite a code section that supports this. (not challenging you – 
it makes sense and I agree)  I have been wondering about SMA’s recommendation 
to parallel two 1/0 cables for a Sunny Island. If the wire sizes and lengths 
are identical, is this acceptable?  Jason SzumlanskiFafco Solar  From: 
re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Nick Soleil
Sent: Wednesday, February 02, 2011 12:05 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Parallel wire runs to increase size  You shouldn't 
parallel wiring that way.  That is not acceptable by code, and it is 
unnecessary.   If the #10 is not sufficient just replace it.  Due to the fact 
that the larger wiring has much less resistance, most if not all of the current 
will flow on the larger wires. Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell: 707-321-2937
Office: 707-789-9537
Fax: 707-769-9037    From: "Starlight Solar, Larry Crutcher" 
<la...@starlightsolar.com>
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Sent: Wed, February 2, 2011 8:00:07 AM
Subject: [RE-wrenches] Parallel wire runs to increase sizeWrenches, Some of our 
business involves repairing poor PV solar installations on recreational 
vehicles. So often we wind up installing a roof junction box and running a 
second PV to controller wire and then replacing the controller to battery wire 
size. For instance, we may find a 10 gauge wire run to the controller. We then 
add #8, #6, #4 or even 2 gauge and parallel to the #10 depending on power and 
distance of the run. My question: Is there a calculator or chart that will tell 
me what the combination of any two wire sizes equate to? example: #10 + #4 = 
X Thanks.Larry Crutcher
Starlight Solar Power Systems
powered by STARLIGHT™  
-----Inline Attachment Follows-----

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




      
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to