Yes, Enphase bonds the DC positive to ground in their inverters.  This allows 
them to work with all modules, including SunPower.

 Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell:   707-321-2937
Office: 707-789-9537
Fax:    707-769-9037




________________________________
From: Brian Mehalic <br...@solarenergy.org>
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Sent: Wed, September 15, 2010 6:19:21 AM
Subject: Re: [RE-wrenches] GEC for Enphase inverters

According to the Enphase website (/support/faqs):

"The Enphase Microinverter manual states that the device is positively 
grounded. 
Don't most PV modules have negative grounds? Is this a problem for Enphase?

Enphase made the decision to positively ground its microinverters to minimize 
corrosion. Because Enphase Microinverters are positively grounded, they are 
compatible with both positively and negatively grounded modules."

Now I couldn't actually find that anywhere in any of their installation 
manuals...but the instructions for "Grounding the System" does say to "Route a 
continuous GEC through each of the Micro-inverters and AC branch circuit 
junction box to the NEC approved AC grounding electrode."  Clearly this 
conductor will function as both the DC GEC and the EGC, too.

Inspectors in Arizona (some of them anyway) have been allowing the DC GEC to 
land on the ground buss in the main service for some time.  I sort of find the 
idea of an irreversible bond a little silly (well especially where the two GECs 
must come together) - I've worked on a lot of systems using only ground rods, 
and the connection to them is often made with the most reversible of connectors 
(an acorn), and usually it is excessively accessible.  And of course the other 
end of the AC GEC is landed on a bus too.

Brian


On Tue, Sep 14, 2010 at 11:09 PM, R Ray Walters <r...@solarray.com> wrote:

It seems to me that William's original question of where does the EGC stop, and 
the GEC begin, all depends on whether the Enphase inverters bond negative to 
ground internally.
>Did we ever get an answer from Enphase?
>
>If they don't, then I think by definition in article 100, we would only have 
>an 
>EGC (no DC GEC, since neither DC conductor is grounded). 
>If they do bond neg. to ground, then from the inverter all the way to the 
>electrode should be an "unbroken" DC GEC, and stopping at the main service 
>ground buss would constitute a prohibited reversible connection. (it seems we 
>should at least bond irreversibly to the AC GEC after it leaves the buss, or 
>sink another electrode for the DC GEC and the array frame as required by 
>690.47(D))
>
>
>Please, somebody flog me with some facts and code, so we can put this dying 
>horsey to bed.
>
>
>R. Walters
>r...@solarray.com
>Solar Engineer
>
>
>
>
> 
>
>On Sep 14, 2010, at 6:31 PM, August Goers wrote:
>
>Hi All -
>> 
>>I would just add that having a good c-tap crimping tool on hand is just about 
>>as 
>>valuable as it gets in the solar business. I remember holding off on getting 
>>one 
>>because of the $200 or $300 price tag but once you have it you won't believe 
>>you 
>>lived without it. The possibilities are almost endless, but we use our 
>>crimpers 
>>to bond our GECs to the other existing GECs all the time. Ctaps almost always 
>>replace wire nuts when dealing with bare copper EGCs. The c-taps typically 
>>cost 
>>less than $5 a pop and always save that much on labor. Most time when we have 
>>a 
>>multiple string inverter installation is makes sense to irreversibly crimp 
>>the GECs together and run one wire back home.  
>> 
>>Greenlee, Panduit, etc make good tools and taps. Let me know if you would 
>>like 
>>part numbers... -August
>> 
>>
>>
>> 
>>On Tue, Sep 14, 2010 at 8:41 AM, Bill Brooks <billbroo...@yahoo.com> wrote:
>>
>>T
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches@lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches..org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>
>
>


-- 
========================
Brian Mehalic 
NABCEP Certified Solar PV Installerâ„¢
PV Online Coordinator
Solar Energy International
Carbondale, CO 81623
http://www.solarenergy.org



      
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to