Chris, We deal with deep wells routinely. Recently we installed a GTWB system for a very enjoyable retired couple. Their needs included the goat milker, sheep barn, two freezers and a fridge, and irrigation well pump, with the system sized for continuous operation in the event of a long-term (i.e. permanent) loss of the grid. This was on one acre in the suburbs south of Albuquerque. We used an XW4548, as it was the only battery-based, 120/240, single-inverter, grid-tie unit available currently. As part of the normal load-reduction process, we determined that the 2hp conventional well pump could be replaced with a 1hp soft-start SQ and have adequate head and flow for their sprinklers. Changing out the pump way more than paid for itself in the amount of inverter capacity we didn't need. I would encourage you to look at both of these related issues carefully as part of this situation: could a smaller pump meet the head and flow requirements of this site, and is a soft-start pump available? Usually, if an inverter or stack of them can't handle a big inductive load like a conventional pump, it's because of the starting surge. I suspect a smaller soft-start pump may be doable in your situation. Allan Allan Sindelar
Hello offgrid Wrenches, I just inherited an off grid system with one
VFX3524
inverter running the home loads, and a 17kW Guardian Generac they use
for
charging (through an X-240 back into the inverter) & to run their
Franklin
3hp 240 VAC well pump, S. F. max amp 17.0 ( rated on its controller) This is a really convoluted system as they have
another
120/240 VAC Transformer to have the inverter talk to the 240 volt
signal the
gen set needs to see. Yikes. So I am proposing to add a second inverter if it
can run the
well pump and eliminate the extra transformer. This will also reduce
gen set
run time in half while battery charging, a big plus with the nice 24V
Hawker
battery bank, 1020 AH at the 6 hour rate. There aren’t any other unusual large AC loads in
the
home, just the fridge, washer, computer, and such. LPG for cooking,
water
heating, clothes dryer. Thanks in advance for all ideas here! Sincerely, Solar
Wind Works |
_______________________________________________ List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org